Advice on a package A/C constantly tripping the breaker

Denwad

Well-known member
Joined
Oct 16, 2012
Messages
375
Location
Chandler, AZ
Hello gentleman I have a Coleman Suncutter with a addon electric heat package ( 59.7 amp draw ) and it constantly trips the 60 amp breaker its attached to.

I've opened it up and inspected the heating elements, no problem there, and i've checked the circuitry and wiring and nothing seems burnt.

its clearly drawing too much current but i haven't a clue why.

any clues where to look?

the model of the packaged a/c unit is 7430A601 and the model of the add on heat package is 7642-9151

i found the wiring diagrams and i will post pictures of what i have found so far , i think its just wired wrong and putting too much current on one pole of the breaker
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
D

Denwad

Well-known member
Joined
Oct 16, 2012
Messages
375
Location
Chandler, AZ
i believe it is 15kw

{EDIT}

I can't get any pictures right now but coming off the breaker into the unit there are two more circuit breakers ( each 60 amp ) and i cycled them both, and now it seems to be running fine.
 
Last edited:

keelan

Well-known member
Joined
Jul 31, 2013
Messages
135
Location
Kelowna, BC
15 kW/240 V=62.5 A

Also, the safe working load for a breaker is 80% of its rating, so 48 A is typically the max for a 60 A breaker.

Working back from the figures you gave us:

59.7 A / 80% = 74.63 A

Seems you'd be more suited to a larger breaker.
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
15 kW/240 V=62.5 A

Also, the safe working load for a breaker is 80% of its rating, so 48 A is typically the max for a 60 A breaker.

Working back from the figures you gave us:

59.7 A / 80% = 74.63 A

Seems you'd be more suited to a larger breaker.

Depends on the type of electrical load. On many strip heaters, the MCA is very close to the breaker size. I was sizing some yesterday at work with an MCA of 44 and a 45 amp breaker.
 

joel63

Well-known member
Joined
Oct 9, 2012
Messages
1,909
Location
Central FL
Are you able set up the heat strips in to 2 stages.
One running 5 kw, and the other at 10 kw?
You would have to run 2 circuits from the power panel to the heater control panel and then use a thermostat with 2 stage heat control.
The installation instructions might cover a set up like this.
 
To avoid these ads, REGISTER NOW!

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
Are you able set up the heat strips in to 2 stages.
One running 5 kw, and the other at 10 kw?
You would have to run 2 circuits from the power panel to the heater control panel and then use a thermostat with 2 stage heat control.
The installation instructions might cover a set up like this.

Good advise.

To the original poster, If the unit still trips the 60A breaker, and you want a quick solution so it works on the existing set up, just diasable one of the three 5kW heat strips. You will still have 10kW and drop the amperage draw. Put a note inside the unit so you will remember in the future what revision was done.
 

crazy wheel

Well-known member
Joined
Feb 26, 2011
Messages
197
15 kW/240 V=62.5 A

Also, the safe working load for a breaker is 80% of its rating, so 48 A is typically the max for a 60 A breaker.

Working back from the figures you gave us:

59.7 A / 80% = 74.63 A

Seems you'd be more suited to a larger breaker.

only if the power wire is sized for it, otherwise the wiring will become the fuse :scared:
 

crazy wheel

Well-known member
Joined
Feb 26, 2011
Messages
197
Hello gentleman I have a Coleman Suncutter with a addon electric heat package ( 59.7 amp draw ) and it constantly trips the 60 amp breaker its attached to.

I've opened it up and inspected the heating elements, no problem there, and i've checked the circuitry and wiring and nothing seems burnt.

its clearly drawing too much current but i haven't a clue why.

any clues where to look?

the model of the packaged a/c unit is 7430A601 and the model of the add on heat package is 7642-9151

i found the wiring diagrams and i will post pictures of what i have found so far , i think its just wired wrong and putting too much current on one pole of the breaker

I think you need a qualified electrician to evaluate the wiring to your heater.

15kw usually requires a larger electrical supply than a 60amp circuit.
I commonly see a 60amp circuit and a 30amp circuit for 15kw
 
OP
D

Denwad

Well-known member
Joined
Oct 16, 2012
Messages
375
Location
Chandler, AZ
@crazy wheel

there is a separate 30 amp circuit, however i was under the impression that its for the a/c compressor section, i guess its necessary for the heater as well.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Under the NEC electric heat is considered continuous and thus should never exceed 80% of the circuit breaker and wire capacity. Also, the NEC does not allow a heater to be protected at more than 60 amps per circuit. That is why larger heaters have more than one circuit supplying them.

Charles
 

crazy wheel

Well-known member
Joined
Feb 26, 2011
Messages
197
@crazy wheel

there is a separate 30 amp circuit, however i was under the impression that its for the a/c compressor section, i guess its necessary for the heater as well.

The a/c will need a circuit as well.
 