High bay light replacement ballast

RedBKM

Well-known member
Joined
Dec 2, 2012
Messages
236
Location
Central Virginia
I've had two high bay lights go out in the last month. I tried bulbs in both but just buzz and no light. I am assuming the ballast are bad. They are about 15 years old.

The number on the light is Hubbell BL400-H8-WH-BI-UPL

Is the ballast inside the white box or do I have to buy the whole unit? My local supplier doesn't carry Hubbell.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
What light source? Phillips Advance has a trouble shooting guide for ballasts, but a clamp on meter is needed to measure amperes, & voltage to see if they are with in the specs listed, be careful & if high pressure sodium or pulse start MH, the igniter needs to be disconnected to avoid meter damage because of the 2500V pulse. Advance & others do have ballast kits for replacement.

Here is a link to Phillips Advance, to find the trouble shooting info.

http://www.usa.lighting.philips.com/connect/advance/index.wpd
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
HID lights have a capacitor and a ballast. Either could have failed. If these are about 15 years old, they are likely probe start (no high voltage pulse) but Norcal's advise is good: be very careful! The ballast output voltage is enough to kill you, and is NOT isolated from ground/neutral!

Oh, and check the bulb socket and wiring. FWIW, my money is on the capacitor, but that's a WAG at best.
 
OP
R

RedBKM

Well-known member
Joined
Dec 2, 2012
Messages
236
Location
Central Virginia
Thanks for the link Norcal but the Philips University is down for maintenance.

HID lights have a capacitor and a ballast. Either could have failed. If these are about 15 years old, they are likely probe start (no high voltage pulse) but Norcal's advise is good: be very careful! The ballast output voltage is enough to kill you, and is NOT isolated from ground/neutral!

Oh, and check the bulb socket and wiring. FWIW, my money is on the capacitor, but that's a WAG at best.

These use a 400W metal halide bulb. Is that considered HID? Is the cap and ballast a unit or are they seperate parts?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
These use a 400W metal halide bulb. Is that considered HID? Is the cap and ballast a unit or are they seperate parts?

The ballast & cap are separate.

Metal Halide is just one HID light source.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta

JoeFin

Well-known member
Joined
Sep 13, 2013
Messages
717
Location
NorCal - where the Rednecks Race
Ballast have a "Service Life" given in hours

A commercial building can easily estimate the number of hours the lights have been in use to make the decision is it time to replace ALL the ballast or are these just random burn outs

Use you ballast model number with the manufacture date stamped or stenciled on the ballast to look up service life of those ballast
 
OP
R

RedBKM

Well-known member
Joined
Dec 2, 2012
Messages
236
Location
Central Virginia
For the future searchers.....

The replacement ballast kit is from Universal. The part number is M400ML5AC4M500K

It bolted right into the housing using the original hardware. Here is a pic of the inside.

2013-12-28%2011.12.43_zpsrgazkq89.jpg
 

Rookie2

Well-known member
Joined
Feb 27, 2013
Messages
1,925
Location
Western Pa.
Usually its the cap. but you have to remove the resister to check it . You have to use an exact value uf and voltage replacement. Go on ebay or on line lighting companies .
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
For the future searchers.....

The replacement ballast kit is from Universal. The part number is M400ML5AC4M500K

It bolted right into the housing using the original hardware. Here is a pic of the inside.

http://i1135.photobucket.com/albums/m629/redbkm/Mobile%20Uploads/2013-12-28%2011.12.43_zpsrgazkq89.jpg[IMG][/QUOTE]

Unless the fixture is GE (they build their own ballasts) a ballast kit works well & installs w/ ease.
 