Grounding at a shed subpanel
tmnutan
I’m running power to my shed and I’ve got a few questions that I’m hoping somebody could help me with. Here’s an overview:
I’m doing a subpanel at the shed. Distance from the main panel (at the house) to the shed is about 100’. Using 10/3 wire (two hots, a neutral, and a ground).
At the main service panel I have a double-pole 20-amp breaker.
At the shed: I have a subpanel for two circuits, either two 20's or a 15 and a 20. I have two 8’ ground rods, 6' apart, connected with #6 wire.
These are my questions:
1) Grounding at the shed Part 1 - Where do I connect the #6 to the subpanel?
2) Grounding at the shed Part 2 - What do I do with the ground that’s coming from the main panel (the bare wire in the 10/3 “feed”)? I don't think it's supposed to be connected to the subpanel, is that right? Should it be connected at the main panel (that wouldn't make much sense to me)?
3) At the shed, should I get a subpanel with a main breaker, one switch that will shut the whole thing down? That seems like overkill if I only have 2 circuits, but I’ve seen it mentioned a few places.
4) GFCI – if I put an outlet on the outside of the shed, does the outlet need to be GFCI, or the breaker, or both?
Thanks very much for any guidance you can provide. I live in North Carolina, FWIW.
Nowater
Southwest Florida
Check your local codes for information about the additional ground rods for your shed. Some codes (inspectors) don't want another ground rod on a residential service.
Your subpanel (every subpanel) will require a ground bar separate from the neutral bar, and the neutral bar should not be bonded (electrically connected) to the panel or to the ground bar. The ground bar is bonded to the panel. You may have to purchase the ground bar, the last one I bought was a few bucks. They look about identical to the neutral bar. If the panel manufacturer supplies a neutral bonding screw, (usually these are green) don't use it on a subpanel.
The ground wire from your 10/3 connects to the ground bar along with all the ground wires from your circuits.
The neutral from your 10/3 connects to the isolated neutral in your panel along with all the neutral wires from your circuits.
I prefer the idea of one main breaker to shut down the entire remote panel, but with only two circuits that may be overkill!
I suggest a ground fault receptacle for each receptacle you want regardless of inside or outside. They have come down in price a lot.
At the main panel, the 10/3 neutral connects to the neutral bar there, and the ground connects to the ground bar there.
I know the separation of ground and neutral in a sub panel is a confusing issue and not intuitive, but it has been this way for many years and is often installed incorrectly.
Highbeam
Mt Rainier foothills, WA
Ditto to the above which is almost word for word the same post I made at the hearth forum where you also posted this exact same question. Cheers!
I was absolutely required to put in separate ground rods at the subpanel in my detached shed.
2ManyProjects
Why such light-duty wire for the feeder cable? It seems to me that if this is worth doing at all, it's probably worth doing in a manner which will not put so severe a crimp in what you can run in that "shed". Further, if (as I suspect) that "10/3 wire" is run-of-the-mill NM-B, how are you planning to get it across that 100-foot gap between the house and the shed? NM-B is NOT rated for underground use, even in conduit.
Even with the light feeder cable, you could go to 30A here without creating a huge problem, at least presuming your measurement is accurate. Technically, this will produce just slightly over the 3% maximum recommended voltage drop at full load; but it is SO close that I would not lose sleep over it.
Exactly what loads do you intend to run off these breakers?
To the Ground bus bar inside the panel; and NOT to the Neutral bus bar, which in turn should NOT be bonded to the Ground (you may need to remove a pre-installed bonding screw to accomplish this, and/or possibly even purchase an accessory part to implement the separate Ground & Neutral busses).
It too connects to the Ground bus bar.
No. Wrong.
It needs to be properly connected at BOTH ends.
With six or fewer branch circuit breakers in the sub-panel, you are not required to provide a "Local Disconnect". That said, it's not prohibited either; and IMCO, it remains a good idea in any case.
Not "both". The outlet needs to be "GFCI-protected". That protection can be supplied by either an integrated GFCI-type outlet, or a GFCI breaker.
You're welcome. But do note that my answers above are NOT geographically specific (save for being USA-centric), and local codes can always override the NEC. So when in doubt, it's always best to check with YOUR local inspector or permit office.
AFAIK, historically the second set of ground rods were not always required, but were never prohibited. And they HAVE been required for awhile, now.
Exactly correct.
Agreed.
Regardless of cost, more than one per branch circuit is a total waste, assuming you wire things correctly.
Also correct.
I agree that this topic seems to foster a lot of confusion; but I really don't understand why. Neutral and Ground are two different things; and BOTH are required, period. It really is that simple.
Highbeam
This came across a bit confusing. Please allow me to clarify and speak up if you disagree.
The neutral bar is not be bonded to the can and the ground bar must be bonded to the can. All grounds land on the bonded ground bar and all neutrals land on the unbonded neutral bar. You are not to connect the neutral bar to the ground bar in the subpanel.
Here's my shed subpanel that is correctly wired for reference.
Highbeam
Oh and it is entirely possible that the OP was running 10/3 UF to this subpanel which is entirely legal, easy, and likely. Underbreakering the feed at 20 amps is also entirely legal and likely.
Myself, I would rather deal with conduit and THWN and I use the largest breaker allowed.
pattenp
Virginia - USA
2manyprojects made a comment about contacting the local inspector.
"You're welcome. But do note that my answers above are NOT geographically specific (save for being USA-centric), and local codes can always override the NEC. So when in doubt, it's always best to check with YOUR local inspector or permit office."
So, 2manyprojects, he should NOT check with the local code official?
2ManyProjects
By all means, be my guest...
I agree completely. ;)
Very possible. But since Type UF-B wasn't explicitly stated, it did not seem prudent to assume that. Either way, I still take the view that if you're going to go to all the work necessary to do this, why self-impose a 30A (or worse, 20A) limit?
HUH?!?
As "pattenp" pointed out (thanks!), that is exactly the OPPOSITE of what I said.