Junkman
Well-known member
I have a 200 amp automatic transfer switch that I am going to install in place of the existing 200 amp manual transfer switch for my genset. The instructions in the automatic transfer switch say that it should be wired with copper wire. Presently, there is aluminum wire going from a disconnect switch in to the manual transfer switch, and then it goes out that box with a 90 degree sweep downward to another 90 degree sweep, under the concrete floor. Then it comes out of the floor with a 90 degree sweep into another disconnect switch. The reason for this is that I added onto the garage, and moved the original service to the new garage. Every time it went underground, and back up, the inspector wanted a circuit breaker disconnect. How difficult will it be to pull the original aluminum wire through the two 90 degree sweeps, and replace it with copper? Since all this change made the original circuit breaker box a sub panel, there is also a #4 copper ground wire in the PVC conduit. The conduit is a 2 1/2" run that is about 30 feet with the 2 90 degree sweeps. I intend to leave the #4 copper wire in the pipe, and just pull the 3 new copper conductors, if this is possible. The wire from the disconnect on the back of the meter to the new transfer switch is very short, so that one shouldn't present a problem. Thanks