Hey guys,
I never threw out my old oven and I was thinking I could use just the oven part to cure powder coated items.
My question is this, we ran a 240 outlet into my garage, but this was before we had plans for a oven so we only ran 10 gauge wire.
If I have NO intentions of running the top range (I even removed the elements already), can I get away with running 20-30 amps to the oven only without causing a house fire? Like a dual 15 or dual 20 and each 110v from its own breaker, will 10 gauge be safe? I am running my air compressor off a 30amp breaker with 10 gauge wire no problem, but the compressor is only 22amps. We have no way of running 8-2 wires without ripping up the sheet rock again.
I never threw out my old oven and I was thinking I could use just the oven part to cure powder coated items.
My question is this, we ran a 240 outlet into my garage, but this was before we had plans for a oven so we only ran 10 gauge wire.
If I have NO intentions of running the top range (I even removed the elements already), can I get away with running 20-30 amps to the oven only without causing a house fire? Like a dual 15 or dual 20 and each 110v from its own breaker, will 10 gauge be safe? I am running my air compressor off a 30amp breaker with 10 gauge wire no problem, but the compressor is only 22amps. We have no way of running 8-2 wires without ripping up the sheet rock again.