Adding a sub-panel - wire question

Chuckster815

Member
Joined
Jan 30, 2009
Messages
9
New to the forum, planning to add a compressor to my garage. Researched adding a sub-panel and feel relatively comfortable, having done some wiring before.

What I don't know is how to figure what size wire to run from the main panel to the sub-panel in the garage. Basically one end of the house to the other, approximately 75 feet. For a 100A sub-panel, what would be required?

Chuck
 
To avoid these ads, REGISTER NOW!

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
Just finished mine. Ended up running 1/0-1/0-1/0-2 AL SER feeder thru 2'' pvc conduit 80' to a 125 amp lug panel. It is fed by a 125 breaker in the main panel and a 50 amp at the sub.8-3 copper in 3/4 conduit from the sub to a disconnect at the compressor.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
New to the forum, planning to add a compressor to my garage. Researched adding a sub-panel and feel relatively comfortable, having done some wiring before.

What I don't know is how to figure what size wire to run from the main panel to the sub-panel in the garage. Basically one end of the house to the other, approximately 75 feet. For a 100A sub-panel, what would be required?

Chuck

Is this an attached garage? Do you want to run conduit or use cable?

Just finished mine. Ended up running 1/0-1/0-1/0-2 AL SER feeder thru 2'' pvc conduit 80' to a 125 amp lug panel. It is fed by a 125 breaker in the main panel and a 50 amp at the sub.8-3 copper in 3/4 conduit from the sub to a disconnect at the compressor.

Same question, attached or detached garage?

If Alum you need 3 - #2 guage and 1 - #6 for ground, again with green insulation for the ground wire.

#2 AL is not 100 amp wire in this scenario. Depending on the whether he uses conduit with individual wires or cable, it can have a max breaker size anywhere from 70-90 amps.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
They have number 2 alum quad wire at the box stores just for this, direct burial or pipe. I don't recall which but one of them had a better wire, there is a difference. One store had 2-2-4-6 and one was 2-2-2-6 and priced better to boot. I usually feed them with a 60A as the breaker is cheap.
 
To avoid these ads, REGISTER NOW!
OP
C

Chuckster815

Member
Joined
Jan 30, 2009
Messages
9
The garage is attached. I do not currently have any conduit, code here does not call for it. If I was to use copper cable would it be 2-2-2-4? I would have a 75' to 80' foot run with 100A sub-panel.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
If I was to use copper cable would it be 2-2-2-4? I would have a 75' to 80' foot run with 100A sub-panel.

Yes, that would work for a 100 amp panel. You can price out 1/0 AL SER too, if you get sticker shock on the copper.

You may need to purchase from a supply house to get these sizes. I believe Home Depot usually only carries #2 AL SER cable.
 

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
Is this an attached garage? Do you want to run conduit or use cable?



Same question, attached or detached garage?



#2 AL is not 100 amp wire in this scenario. Depending on the whether he uses conduit with individual wires or cable, it can have a max breaker size anywhere from 70-90 amps.

Aceman, my shop is detached
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Just finished mine. Ended up running 1/0-1/0-1/0-2 AL SER feeder thru 2'' pvc conduit 80' to a 125 amp lug panel. It is fed by a 125 breaker in the main panel and a 50 amp at the sub.8-3 copper in 3/4 conduit from the sub to a disconnect at the compressor.

Aceman, my shop is detached

The reason I asked is that the codebook doesn't allow SER underground. Something like this would of been more appropriate:
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet15
 

mad57

Well-known member
Joined
Jan 30, 2009
Messages
1,698
Thats what im going to use now 2-2-2-4 aluminum with a 8 space 100amp breaker sub panel $36 bucks... to go about 70 feet its cheaper than the copper wire from there ill branch off the sub panel to my welder . plasma .. lift.. compressor ..with 6-3 copper... forgot to add i have a 200 amp square d box... all the parts are at the hd and are cheaper than my local elec supply.. although the elec supply priced me .89cents a foot for 6-3 copper where hd was 2.64 a foot by the foot. if you buy there 125 ft roll its $136.00 so some savings there. good luck sounds like your on the right track mike.

The garage is attached. I do not currently have any conduit, code here does not call for it. If I was to use copper cable would it be 2-2-2-4? I would have a 75' to 80' foot run with 100A sub-panel.
 