Number of outlets per circuit

myfinishingtouch

Well-known member
Joined
Aug 23, 2013
Messages
52
I'm wiring up my shop and plan to have 110 outlets every 5 feet on the walls. How many should I put on one circuit? I'm using 12 gauge wire.
Thanks
Dave
 
To avoid these ads, REGISTER NOW!

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
849
Location
In between MA and PA
Yup, where do you live. In the US there is no limit for residential. That may not be the best practice though.

What do you plan for uses?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
There is no limit in residential, in non-residential each one is counted as 180 VA each. One is pretty safe by limiting them to 10 receptacles max per circuit.
 
OP
M

myfinishingtouch

Well-known member
Joined
Aug 23, 2013
Messages
52
This is a residential detached garage in Shreveport, LA. I don't envision having multiple things running at once but am not sure where I'll end up years from now. The garage is for my retirement woodworking hobby.
Thanks,
Dave
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,927
Location
Niagara Region, Ontario, Canada
Wire & breakers are relatively cheap compared to the aggravation experienced down the road when you don't have enough circuits & keep blowing them.
I would consider putting each wall on a separate circuit
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,274
Location
The romantic hills of central Umbria, Italy,
I always ran no more than "one wall" per 110 circuit, lights on their own, and the big stuff on its own leg (sometimes necessary because of the 220 requirement). I used to have access to cheap or freebie electrical sstuff, so I could add as I wanted - one place (in Berkeley, years and years ago) I had what would look to a pro as a spaghetti factory... altho nothing ever burned (thank the Gods!) I knew it wasn't right...

I was told no more than 8 outlets per circuit running 12-2 on 20 amp circuits... so from then on I've tried to stick to it. The reasoning is you'll never have *all* of those outlets hot and drawing 100% at once. Lights are easier, as there's no variable - you know what those fixtures will draw, so you can go either 14 or 12, plan for 150% of their draw, and stay safe.
 
To avoid these ads, REGISTER NOW!

plow

Well-known member
Joined
Feb 12, 2013
Messages
1,024
Location
Louisiana
This is a residential detached garage in Shreveport, LA. I don't envision having multiple things running at once but am not sure where I'll end up years from now. The garage is for my retirement woodworking hobby.
Thanks,
Dave

Hi Dave, Bistineau and I are your neighbors. I live at the end of Colquitt Rd. area, Bistineau..........Well you can guess where he lives.:beer:

Btw, I did walls on each ckt. and my 220's by themselves.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
"Best Practice" in my local is no more than 8 per circuit to allow for expansion. I would recommend no more than 13 on a circuit with 12 wire.
 
OP
M

myfinishingtouch

Well-known member
Joined
Aug 23, 2013
Messages
52
Thanks all. I think I'm going one circuit per wall for the 110 and need to think on how to do the 220. And then how many 3-phase circuits to run. I have a mix of single and 3-phase tools run from a phase converter.

plow. My son and I ride our ATVs out at Highlifter regularly.

Dave
 

Dick in Wisconsin

Well-known member
Joined
Mar 3, 2012
Messages
3,048
Location
Shawano, Wisconsin
I presume you're going with 20 amp circuits for the outlets.

Consider putting in a double box and four outlets at each location. Don't forget the GFCI's on each circuit. Don't try to scrimp and use the cheap contractor outlets, get the better grade, you'll appreciate it in the long run.

When does the pig tail vs backstab vs backwire debate start?
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Thanks all. I think I'm going one circuit per wall for the 110 and need to think on how to do the 220. And then how many 3-phase circuits to run. I have a mix of single and 3-phase tools run from a phase converter.

plow. My son and I ride our ATVs out at Highlifter regularly.

Dave

I've only hooked up one phase converter and it was for a single unit, a mixer. Is there a max amp on yours,so say it's 60 amps you could power up a 60 amp 3 phase panel and then wire up the equipment like a normal hookup. I will tell you 3 phase stuff isn't cheap
 

plow

Well-known member
Joined
Feb 12, 2013
Messages
1,024
Location
Louisiana
Thanks all. I think I'm going one circuit per wall for the 110 and need to think on how to do the 220. And then how many 3-phase circuits to run. I have a mix of single and 3-phase tools run from a phase converter.

plow. My son and I ride our ATVs out at Highlifter regularly.

Dave



pass it every day.
 