Convert a 220 breaker into 110?

dmk0210

Member
Joined
Apr 15, 2014
Messages
6
I have a circuit that once had a 220V baseboard heater on it. I've removed the heater and plan to remove the wiring from the breaker panel.

I need a 110V circuit for overhead lighting. Is it possible to remove the 220V breaker and replace with 110V breaker, then wire up a single 110 circuit?

I read about multiwire branch circuits and the associated caveats, but I don't want two circuits, just one.

BTW, I'll do all the overhead wiring and lights, but I plan to get an electrician to replace the breaker and connect the wiring to the panel. I just want to make sure this is doable before I start.
 
To avoid these ads, REGISTER NOW!

bcassel

Member
Joined
Jan 13, 2014
Messages
23
Location
Northern California
If it is like most 220 breakers, it is just two 110 breakers hooked together, one to each side of your service. You can make it two 110s by just removing the clip that holds them together.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The short answer is yes. The 220V DP breaker used two stabs in the panel whereas the 110V SP breaker will only use one stab leaving you an extra space for another SP breaker if needed.

Edit: Don't modify the 220V breaker, besides it may be to large of an amperage breaker for your new circuit.
 
OP
D

dmk0210

Member
Joined
Apr 15, 2014
Messages
6
Thanks for the quick replies guys!

That is good news.

When I Googled, I found all sorts of stuff on multiwire branch circuits and the dangers of the neutral getting disconnected. It didn't sound very good at all.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
The 240 Volt circuit, in all likelihood, doesn't have a neutral conductor.

Just replacing the circuit breaker wouldn't do it, because the 120 Volt circuit requires a neutral, and you can't remark the 2nd (existing) wire unless it is a #4 or larger
 
Last edited:
OP
D

dmk0210

Member
Joined
Apr 15, 2014
Messages
6
The 240 Volt circuit, in all likelihood, doesn't have a neutral conductor.

Just replacing the circuit breaker wouldn't do it, because the 120 Volt circuit requires a neutral.

How can I verify that?

On the heater side, I had three conductors: white, black and ground.
 

Professur

Well-known member
Joined
Apr 7, 2010
Messages
3,911
Location
Mo-Ray-Al, K-bec, Ka-Na-Da
On the 220V breaker you will have two wires. Take one and put it on the terminal of the new 110V breaker. Take the other one and attach it to the neutral bus bar. Make sure there's nothing else on that circuit before you monkey with it tho.
 
To avoid these ads, REGISTER NOW!
OP
D

dmk0210

Member
Joined
Apr 15, 2014
Messages
6
OK, I think I see. So I plan to run new wiring for the lights to my breaker panel.

If I disconnect the old wiring, and replace the breaker, then I should be able to wire up the new 110v wiring with a neutral?
 

James_B

Well-known member
Joined
Jun 24, 2013
Messages
674
Location
Nova Scotia, Canada (started in Brisbane, Australi
If it is like most 220 breakers, it is just two 110 breakers hooked together, one to each side of your service. You can make it two 110s by just removing the clip that holds them together.
Don't count on that. I just took apart a Siemens 220V double breaker as one side had gone bad, and I wanted to see if I could cut the good side free so it could be used as a 110V breaker.

I discovered an internal mechanical linkage between the two sides as well as the joining bar connecting the levers. Pulling out the internal mechanical linkage and removing the lever join would have let it work fine as a single 110V breaker, but there was a large hole in the each of the two adjoining faces of the double breaker in order to accommodate the internal mechanical linkage.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
If you already have a white wire in the cable then connect the white wire to the neutral bar, and the black to the breaker.

Buy a new single pole breaker and a filler plate to install in the opening left in the panel cover, and you're good to go.
 
OP
D

dmk0210

Member
Joined
Apr 15, 2014
Messages
6
If you already have a white wire in the cable then connect the white wire to the neutral bar, and the black to the breaker.

Buy a new single pole breaker and a filler plate to install in the opening left in the panel cover, and you're good to go.

Awesome.

Thanks guys! :)
 

TheEquineFencer

Well-known member
Joined
Jan 15, 2009
Messages
9,278
Location
Farmville, NC 27828
I'd install a new Single breaker, remove the old wiring from the old double pole breaker and cap the ends of those two wires with a wire nut and leave them in the panel. Then I'd install all new wiring. That way you leave nothing to the unknown. Don't forget to install a block off plug for the open breaker hole.
 