Conduit Size Chart
Bearkat
Getting ready to wire my workshop which should be completed next week. Is there a chart for how many 20 amp circuits I can run in each size of metal conduit? I want to run two for the lights, with one pipe coming off of the panel- is there room for a couple plug circuits as well if I step up to 3/4? Also, I need to make a shopping list so I will need to know the different sizes I need at each point. Also, do I need to run multiple ground wires, or can all circuits in the line tie into 1 ground?
Beemer533
Syracuse, NY
Here is a pdf with the fill allowances..
Here is a calculator.
I think these are a couple years old, but I don't think fill maximums have changed..
I think you can share an egc as long as it is sized correctly, but I'm sure someone will chime in that knows what code actually says.
JohnX14
Boston 'burbs
If you mean EMT (Electrical Metallic Tubing) and are using #12 THHN you can fit the following number of condutors in each size:
1/2" - 9
3/4" - 16
1" - 26
1 1/4" - 45
1 1/2" - 61
Obviously you need 2 condutors for a 120 or 240 volt circuit and 3 conductors for a 120/240 V circuit.
But you also have to derate the ampacity of #12 based on the number of circuits using table 310.15(B)(3)(a) for more than 3 current carrying conductors in a raceway. (Though you begin your derating based on #12 having an ampacity of 30A)
There are other factors that may require additional derating.
There is not a one stop chart to explain what you are trying to accomplish. But what I listed above are the 2 most common considerations. If you give me more specifics of what you want to install I can answer better.
JohnX14
Boston 'burbs
Yes they can share a grounding conductor. They can even use the raceway as the ground, but I would not advise it. (Perfectly legal, but problem if even one screw is not properly torqued)
Bearkat
Thanks for the iput. My goal is to only have a few runs of Conduit coming off of my panel and splitting them down the line. I plan to run all 20 amp circuits for plugs and lights. As an example, I would like one run with both light circuits as well as a plug circuit. I could have junction boxes along the wall to drop plugs and run to lights. same thing on the other side with 3 different plug circuits.
JohnX14
Boston 'burbs
Sounds like you can run 3/4" in each direction. You can either stay 3/4" for everything or drop down to 1/2" if you want. The price difference is so little I'd stay 3/4 as it looks a little better. For this few circuits even with derating, you can stick with #12.
Charles (in GA)
50 mi south of Atlanta
You are better off with more pipe runs, and fewer circuits in the pipe. One reason is that it is extremely difficult to pull additional wires in a pipe after the originals have already been pulled, You either have to plan well ahead and pull all of them at once (how many spools of wire do you have :eyecrazy: )
One limiting factor is that more than 9 current carrying wires in a conduit triggers derating for all of the wires in the conduit.
I ran lots of ½ EMT and generally did not pull over four current carrying wires plus grounds, in the conduit. Typically I have three receptacles on a circuit.
Charles
Just a little bit of my "mess 'O pipes".................... and its been added to since this pic was made...............
Charles (in GA)
Yes, we've had that argument before. I agree with you, run grounds, then if the conduit becomes separated for whatever reason, or doesn't make good contact at the panel, you still have a ground. Others go "you are wasting wire, you don't need it, it won't do any good, blah.... blah....." I'm in the run the ground and never worry camp.
Charles
alfredeneuman
Fullerton, CA
Yes an EGC can be shared. It must be the same gauge as the largest ungrounded conductor!!
It can be shared but it needs to be sized to the proper ground wire for the biggest circuit in the conduit, not the biggest ungrounded conductor.
#14 for 15 amp circuits
#12 for 20 amp circuits
#10 for 30 - 60 amp circuits
#8 for over 60 - 100 amp circuits
#6 for over 100-200 amp circuits
TheEquineFencer
Farmville, NC 27828
Personally, if possible, I'd do my runs in 3/4 and stay away from 1/2 EMT, 3/4 is easier to pull wire through even after you have other circuits pulled with a good fish tape. I just added a 140 foot circuit of wire through a 3/4 conduit that I already had two other circuits pulled through, it was easy. I do most of my offsets on 30* when possible. Speaking of fish tapes, I'm not sure if all tapes are the same, but the Klein I have has the feet marked on the tape, it makes figuring wire lengths easy.
Bearkat
Thanks for the info everyone. I think the end result will be a mixed bag, as I expected. Pics to come hopefully sooner than later. They should start standing steel tomorrow.
wyliesdiesels
Modesto, CA
Youre right. Im not sure where i came up with that.