So I'm in the process of buying our first new (to us) home. It has a 24x60 detached garage that has been upgraded by the previous homeowners son. He's lets just say, "adaptable" in his definition of what code standards are. The garage is 30 feet from the main panel. He has somehow run a 2 wire line from the main 200 amp service partially underground to a sub panel in the garage. Its supposedly wired for 120? Anyway, i'm a little confused as to how that is possible with the given wire. Here is a picture of what the wire is. Can anyone tell me if this is correct?

IMG_1759.jpg
 
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
You don't give enough information about the breaker in the main panel to allow an answer. Take a picture of the main panel's breaker feeding the garage and you may be able to get a good answer.

It is possible (possible!) that it is technically correct, but perhaps not going to allow much power to the garage. As 10 AWG, it would be good for about 30 amps maximum.
 

Scott65

Well-known member
Joined
Aug 1, 2011
Messages
139
Location
Green Bay, WI
Technically correct but undersized to meet any serious power demands you may have in a shop. 30 amps is the max as indicated- hardly enough for a lighting circuit and a loop of outlets. I have a 60 amp sub panel in my garage and it is fed with 4awg, might be overkill, but easier to do right the first time.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
51,143
Location
Northern Central Ohio
It's not the size of the wire that scares me, it's the "partially underground" statement that does. Sounds like something half assed.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Basically all you have is a 30 amp 120 volt sub panel so you can prob do two 15 amp circuits. Wire is rated for direct burial but not made to be layed on top of the ground
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
So I'm in the process of buying our first new (to us) home. It has a 24x60 detached garage that has been upgraded by the previous homeowners son. He's lets just say, "adaptable" in his definition of what code standards are. The garage is 30 feet from the main panel. He has somehow run a 2 wire line from the main 200 amp service partially underground to a sub panel in the garage. Its supposedly wired for 120? Anyway, i'm a little confused as to how that is possible with the given wire. Here is a picture of what the wire is. Can anyone tell me if this is correct?

IMG_1759.jpg

What is it that you're confused about? That is a 10/2 NM wire capable of 30a @ 120v. Did u mean its wired for 240v?

It's not the size of the wire that scares me, it's the "partially underground" statement that does. Sounds like something half assed.

The wire is UF-B so its rated for direct burial.
 

Executive

Well-known member
Joined
Jun 29, 2012
Messages
77
The wire you picture is capable of 30 amps. It is also capable of 120 volts or 240 volts. If used for 240 volts, it will not have a grounded conductor designed in the circuit and will be very limiting as to what you connect.

The most likely situation is that it is 120 volts. It should not supply a panel in the detached garage. It should originate in a single pole GFCI circuit breaker, specifically because of the limited burial depth of the cable. (NEC T300.5)

I would plan to correct this wiring if you decide to purchase the property.


Chris
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
The wire you picture is capable of 30 amps. It is also capable of 120 volts or 240 volts. If used for 240 volts, it will not have a grounded conductor designed in the circuit and will be very limiting as to what you connect.

The most likely situation is that it is 120 volts. It should not supply a panel in the detached garage. It should originate in a single pole GFCI circuit breaker, specifically because of the limited burial depth of the cable. (NEC T300.5)

I would plan to correct this wiring if you decide to purchase the property.


Chris

Maximum overcurrent protection is 20 amperes, 120 volts & must be residential to be allowed to be buried 12" in addition to being GFCI protected.

See NEC table 300.5 column 4.
 

Executive

Well-known member
Joined
Jun 29, 2012
Messages
77
Maximum overcurrent protection is 20 amperes, 120 volts & must be residential to be allowed to be buried 12" in addition to being GFCI protected.

See NEC table 300.5 column 4.

100% accurate.

And your point is?


Chris
 