Planning a circuit and wanted to run it by someone. Lights and fan on one circuit.
6 fixtures with 6 32w T8 bulbs
3 fixtures with 4 32w T8 bulbs
48x 32w bulbs = 1536 watts total
1536w/120 volts = 12.8Amps Lets call it 13amps
3 ceiling fans that draw .9amp each. = 3amps.
with a 20amp breaker I'll have 4 free amps, well within the 80% rule.
Am i thinking this out correctly?
Also on the ceiling fans. I bought a controller for them. Wiring Diagram attached.
My thought is that i'll have a MC cable 12/2(with ground) feeding the circuit to the 3 gang switch box. That will power both light switches (6 on one, other 3 on the other).
Power will feed to the controller as well. My thought was to ground the controller and the fans at each box. I want to use MC cable 14/3(with insulated ground) to provide my 4 wires from switch to the first fan and on down the chain to the remaining fans. Since the insulated ground will not be used as a ground, i'll mark it with tape at the exposed ends.
Will that work for my install?
Anybody make a 14/4 mc cable?
6 fixtures with 6 32w T8 bulbs
3 fixtures with 4 32w T8 bulbs
48x 32w bulbs = 1536 watts total
1536w/120 volts = 12.8Amps Lets call it 13amps
3 ceiling fans that draw .9amp each. = 3amps.
with a 20amp breaker I'll have 4 free amps, well within the 80% rule.
Am i thinking this out correctly?
Also on the ceiling fans. I bought a controller for them. Wiring Diagram attached.
My thought is that i'll have a MC cable 12/2(with ground) feeding the circuit to the 3 gang switch box. That will power both light switches (6 on one, other 3 on the other).
Power will feed to the controller as well. My thought was to ground the controller and the fans at each box. I want to use MC cable 14/3(with insulated ground) to provide my 4 wires from switch to the first fan and on down the chain to the remaining fans. Since the insulated ground will not be used as a ground, i'll mark it with tape at the exposed ends.
Will that work for my install?
Anybody make a 14/4 mc cable?