This is more theoretical than actual.
Say you have a location with 3 wire 240v, no neutral, but you need 120v load at that location. Replacing the 3 wire with 4 wire is not practical.
In the "old days", I would just connect the 120V load to one hot and use the ground for neutral.
If I put in a 240/120v transformer, I now have a hot and a neutral, but can I use the ground from the 240v side of the transformer ? This ground is not bonded to the 120V neutral. Can I bond it at the transformer ?