3 wire 220v into a 4 wire receptacle

summit151

Well-known member
Joined
Jul 24, 2013
Messages
69
Hello i am in the middle of wiring my shop. I would like to put one main 220v plug in for a welder and a air compressor. But to run my welder i need a 4 wire 40 amp plug and the air compressor is only a 3 wire 20 amp 220. The air compressor will always be plugged into and i just want to unplug it and plug in the welder when I need it. My question is can you safely run a 3 wire 220 off a 4 wire receptacle?
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,218
Location
SE MI
... to run my welder i need a 4 wire 40 amp plug and the air compressor is only a 3 wire 20 amp 220.
...
My question is can you safely run a 3 wire 220 off a 4 wire receptacle?

Yes. Install a 4 prong plug on the compressor. Do not connect anything to the neutral terminal in the plug.
 
OP
S

summit151

Well-known member
Joined
Jul 24, 2013
Messages
69
Ok that is what i was planning on doing. Just making sure it will no affect anything
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Just do the right thing and install the proper circuit for each. They are two different animals.

Are you SURE the welder requires a 4-wire circuit?
 
OP
S

summit151

Well-known member
Joined
Jul 24, 2013
Messages
69
sorry yes it is a 50 amp stove receptacle. what is the main reason why you can not use a 20 amp compressor on it to?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,218
Location
SE MI
sorry yes it is a 50 amp stove receptacle. what is the main reason why you can not use a 20 amp compressor on it to?

The pigtail from the plug to the motor and the wire inside are rated for 20A. If for some reason they start drawing much more than that, but less than the circuit breaker/fuse, they will overheat and could catch fire.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The pigtail from the plug to the motor and the wire inside are rated for 20A. If for some reason they start drawing much more than that, but less than the circuit breaker/fuse, they will overheat and could catch fire.

The wire needs to be heavy enough to be connected to the 50A,, which would be a number 12. The breaker in this case des not provide for overheat or overload, this is the job of the thermal overload and by design in the fact that the unit only draws 20A,,, it comes with a cord that wont be overloaded by the unit.
The breaker here is an off/on switch and for short circuit protection which involved hundreds,,, or in some cases thousands of amps in a fault.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,218
Location
SE MI
Old School. This will solve your problem (if you can find one). Cooper-Bussmann SKA. You can even use "screw in" breakers.

EDIT: Wow, found one on eBay cheap !
 

Attachments

  • Capture.JPG
    Capture.JPG
    24.4 KB · Views: 8
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Welder circuits have special rules for sizing wire and breaker and are based on duty cycle. Highly unlikely welder would need a neutral unless maybe it has a spool gun or some other 120v device. We need to know the model of the welder to give a proper answer.

Circuit for Compressor on the other hand is sized based on motor HP. We need to know HP rating or compressor model to give a proper answer!
 