romex in conduit or not?

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
U.F. Cable and Romex are not the same thing. Romex is actually just a trade nam for nm cable (nm stands for non metallic sheath)
Romex was/is a major manufacturer of nm cable. Nm and uf cable are recognized in two different articles in the code book.
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Done what? NM is an assembly, so when you strip the outer cover, you have no idea what type of conductor is left. While it is common to use it as a quick alternative to THHN when none is available, it is a violation. What is hard to believe, is that an electrical inspector would require an electrician (Eaglewolf?) to do this questionable violation to correct the use of NM in conduit, when there is no code reason to do so
We strip the sheathing from the part below the joists that will be inside the pipe,I normally leave between 6" and 1' of sheathing inside the pipe.
If its starting inside of a junction box and continuing through pipe to another box then its done in thhn of course,but youre talking about 2 different situations.:)
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,582
Location
Fullerton, CA
The Romex name was originally owned by the Rome Cable Co. for it's NM cable.

Now it owned by Southwire, and is copyrighted. Southwire actually issued a memo recently that demanded when the is referred to in a setting such as Forums it be referred to as: Romex®. (alt+0174), which went largely ignored.

NM's construction is completely different than UF cable. UF does not have a paper filler, which wicks water. NM has no protection against UV, and has a tendency for the jacket to degrade when exposed to the rays of the Sun. NM also is not mildew resistant, unlike UF.

It's called UF in California, too.
 
Last edited:

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
We strip the sheathing from the part below the joists that will be inside the pipe,I normally leave between 6" and 1' of sheathing inside the pipe.
If its starting inside of a junction box and continuing through pipe to another box then its done in thhn of course,but youre talking about 2 different situations.:)

Yes we are
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
U.F. Cable and Romex are not the same thing. Romex is actually just a trade nam for nm cable (nm stands for non metallic sheath)
Romex was/is a major manufacturer of nm cable. Nm and uf cable are recognized in two different articles in the code book.

Actually as alfed pointed out, Romex is a type of nm-b cable made by southwire.

Really? never heard it called direct bury romex. In Maine its UF

Actually, its code name is uf-b but people usually drop the b just the same as with nm-b.

A google search reveals that others call it direct bury romex as well!
 

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland

It was a joke but also kind of true. I saw some drop cords run through white pvc, probably 150'. The installer cut all the ends off the cords and wrapped the joints in electrical tape (no wire nuts). The pipes were strapped but drooping across the walls in U shapes. We came in, tore it all down, and ran EMT in its place.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
U.F. Cable and Romex are not the same thing. Romex is actually just a trade nam for nm cable (nm stands for non metallic sheath)
Romex was/is a major manufacturer of nm cable. Nm and uf cable are recognized in two different articles in the code book.

Romex® was a brand of General Cable for many years until Southwire bought them they are still the owner of the trademark.



NM-B means it's has 90 degree rated conductors, this change occurred in the mid 1980's but ampacity is based on the 60 degree rating, NM is the earlier marking.
 

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
I did the Google search as well. Walmart, Sears, Home Inspector. and DIY Forums aren't really credible sources, much less experts.

In the trades, it is common to refer to UF as direct bury and NM as romex, even though it is not correct. But you never hear "direct bury Romex" in these parts.
 