Will this breaker work for garage heater??

rawfish

New member
Joined
Oct 25, 2014
Messages
4
Hi there :D

I have an existing GFCI 50 amp breaker that I use for my hot tub in the summer [its not used in the winter] and I just bought a 7 kw electric heater for may garage, is there any harm in using the existing 50 amp breaker or do I need to use a 40 amp breaker for this heater??

I "think" I am ok to use the 50 amp breaker but not completely sure.

Thanks:beer:
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,877
Location
oregon
Kinda depends on whether the heater is fused at the heater and if the wire from the heater to the fuse is rated for 50a or better. The breaker is there to prevent the WIRE from being overloaded. What does the heater manual say?

lg
no neat sig line
 

CWO4GUNNER

Well-known member
Joined
Aug 17, 2014
Messages
229
Location
BHC AZ
Unless that 7kw load has its own internal built in protection (breaker fuse), then you will certainly need the minimal size available breaker (40a) or fuse at the source to protect it. Because it is wired to a 50a protected source unless you protect that appliance as stated, the appliance will be damaged if an overload occurs ant the 50a protection will not open.
 
OP
R

rawfish

New member
Joined
Oct 25, 2014
Messages
4
Its actually a 6KW heater . Sorry my mistake saying it was 7 kw.

Sooo this is a 6 KW pro point shop heater. I looked thru the manual and don't see and y reference to a fuse in the heater it self.
Is says " Adjustable thermostat, Hi/Low switch and auto reset overheat protection. Adjustable tilt and louvers to direct heat where you need it most. "

Do I require a 40 amp breaker then or something else??

This is the unit I have:
http://www.princessauto.com/pal/en/Unit/6000W-Shop-Heater/8553521.p
 

CWO4GUNNER

Well-known member
Joined
Aug 17, 2014
Messages
229
Location
BHC AZ
According to the math a 220v /6kw load should be protected by a source a providing protection device of 27a minimal and 33a recommended.
 
To avoid these ads, REGISTER NOW!
OP
R

rawfish

New member
Joined
Oct 25, 2014
Messages
4
got it. Do I need a GFCI breaker? The wire if running from my house to my garage underground.
 