Thanks have found most parts still available except for the burner manifold and since the price is only $150 for this unit if it works can afford to fix if the main valve is no good or other electrical items.
I do have a venting question on this heater can I vent it horizontally out a side wall or should it be vertical being it doesn't have a vent fan?
Not really, the unit is UL Listed, as an assembly. That assembly was listed with a verticle vent. Now, will it work vented horizontally... Yes, with a horizontal vent cap.
Now you can go horizontally thru the wall (pitched slightly up hill) then turn up vertically to a point above the roof. As for height above the roof, there should be no obstruction horizontally (the roof) within 10'. Many think you have to be higher that the peak, no so.
Why would it need a burner manifold? That is basically a piece of schedule 40 pipe drilled and tapped to screw in the burner orfices. Not a part that would ever where out????
As for operation controls, a operating klixon controller to set discharge air temp, wired in series with a high limit klixon controller set to shut the gas off at a too high condition. Many of the old units had the fan start on a call for heat and shut down when temp. Was satisfied. Newer units start the fan when the exchanger reaches a set temp and continue after burner shutdown until the exchanger reaches a cool down temp. (Another spdt klixon with an adjustable dead band.
All pretty easy stuff and klixon switches cost about $10-15.
And gas valve...$100-125.
So be careful if it needs to many parts, as you could quickly get to the price of a new unit!