Is it worth installing modine heater PA105AB

Joined
Oct 1, 2014
Messages
14
Location
NW Wisconsin
Picked up this heater for my 20x30 garage don't have to pay for it til I know it works disassembled heater cleaned and inspected looks ok have no cracks should I take the time to or look for something else
 

Attachments

  • image.jpg
    image.jpg
    140.9 KB · Views: 72
Last edited:
To avoid these ads, REGISTER NOW!

warren57

Well-known member
Joined
Nov 4, 2011
Messages
103
Location
Lochbuie, CO
Of course it's worth installing! You just saved $300-500 bucks.
Good find. Parts are no problem. May not be as high efficiency as a new unit, but the price is right.
Mo dine is a good brand and our shop works on everything, moline and Rheem have a lot of 20+ year old units running fine.
 
OP
D
Joined
Oct 1, 2014
Messages
14
Location
NW Wisconsin
Thanks have found most parts still available except for the burner manifold and since the price is only $150 for this unit if it works can afford to fix if the main valve is no good or other electrical items.

I do have a venting question on this heater can I vent it horizontally out a side wall or should it be vertical being it doesn't have a vent fan?
 

warren57

Well-known member
Joined
Nov 4, 2011
Messages
103
Location
Lochbuie, CO
Thanks have found most parts still available except for the burner manifold and since the price is only $150 for this unit if it works can afford to fix if the main valve is no good or other electrical items.

I do have a venting question on this heater can I vent it horizontally out a side wall or should it be vertical being it doesn't have a vent fan?

Not really, the unit is UL Listed, as an assembly. That assembly was listed with a verticle vent. Now, will it work vented horizontally... Yes, with a horizontal vent cap.
Now you can go horizontally thru the wall (pitched slightly up hill) then turn up vertically to a point above the roof. As for height above the roof, there should be no obstruction horizontally (the roof) within 10'. Many think you have to be higher that the peak, no so.
Why would it need a burner manifold? That is basically a piece of schedule 40 pipe drilled and tapped to screw in the burner orfices. Not a part that would ever where out????
As for operation controls, a operating klixon controller to set discharge air temp, wired in series with a high limit klixon controller set to shut the gas off at a too high condition. Many of the old units had the fan start on a call for heat and shut down when temp. Was satisfied. Newer units start the fan when the exchanger reaches a set temp and continue after burner shutdown until the exchanger reaches a cool down temp. (Another spdt klixon with an adjustable dead band.
All pretty easy stuff and klixon switches cost about $10-15.
And gas valve...$100-125.
So be careful if it needs to many parts, as you could quickly get to the price of a new unit!
 
Last edited:
OP
D
Joined
Oct 1, 2014
Messages
14
Location
NW Wisconsin
Don't think it really needs anything just a cleaning I just found that was the only part not available anymore that's all thanks for the helpful info warren
 

lynnbilodeau

Well-known member
Joined
Jun 4, 2013
Messages
813
Location
Oklahoma
I have a similar heater (Modine PA150A) already mounted in a large garage. There is no venting. I realize if I run it very much, I am probably dumping carbon monoxide into the air, so I would like to vent it.

Can I run approximately 12 foot horizontal with a slight pitch up, then go up the wall and out the roof? Do I need some kind of power vent, or will simply running vent pipe work OK?

Thanks for any help.
 

sms1974

Well-known member
Joined
Jul 9, 2014
Messages
210
Location
Grafton Ohio
Sounds like you've got it figured out for the most part...

I will just throw this out there, remember the air that goes up and out the vent (exhaust) has to be replaced with air coming back in to the space. granted a lot of garages / shops are not all that tight but I have seen several problems arise when you don't have a combustion air make up....
 

Mr_P

Well-known member
Joined
May 29, 2015
Messages
557
Location
Tinley Park, IL
Hey Duramax Junkie. 11+ year follow up here... How did the install go if you did go thru with it? And also, if installed, how has it held up over the years?
 
To avoid these ads, REGISTER NOW!

Mr_P

Well-known member
Joined
May 29, 2015
Messages
557
Location
Tinley Park, IL
Touché. I wonder now if he ended up going with a newer unit after all. I seen one pop up for sale near me for $60, but not sure if I want to deal with it.
 

beltfeed

Well-known member
Joined
Jan 22, 2006
Messages
228
Location
USA
First thing I would do is spend a little time taking the sheet metal off the outside enclosure and look at the heat exchangers condition. If it looks questionable, junk it.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,836
Location
NW Iowa
Touché. I wonder now if he ended up going with a newer unit after all. I seen one pop up for sale near me for $60, but not sure if I want to deal with it.

If it's in ok shape, the next biggest thing is the size. These old heaters are often pretty big. If you have a small insulated garage, you aren't going to be happy.

Natural draft requires a vertical chimney. When I did mine I didn't want a hole in the roof. I went through the sidewall then used a tee to go vertical outside the building. Having the majority of the chimney outside is not ideal by any means but it's worked ok for my use.

I saved an 70% 125,000 btu furnace that I used in my 28x38x9 lined but uninsulated garage. I did convert it to electronic ignition with used part's. Works pretty well but last fall I did save a 75,000 80% furnace that I might swap in if I get the urge.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,015
Location
Peace Valley,mo
Thanks have found most parts still available except for the burner manifold and since the price is only $150 for this unit if it works can afford to fix if the main valve is no good or other electrical items.

I do have a venting question on this heater can I vent it horizontally out a side wall or should it be vertical being it doesn't have a vent fan?
Horizontal vent can be done but needs a flue bootster fan and a safety control is fan doesn't run. Cost more that the heater. CJ3 model
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,836
Location
NW Iowa

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,015
Location
Peace Valley,mo
We had a guy put one on the boiler where I go to church. I never have really liked the thing, should have just lined the chimney. Some of it's install issues but gravity is simple and works.
Guess i installed 10 in span about 25 years on natural gas boilers. From 500k to 2 million btu boilers. With a airflow switch and thermal switch mounted inside the draft hood. Had one fan fail motor locked up pressure switch shut the boiler down. They were all Tjernlund brand. Thought they were well made.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,854
Location
Fargo, ND
We had a guy put one on the boiler where I go to church. I never have really liked the thing, should have just lined the chimney. Some of it's install issues but gravity is simple and works.


When I was selling HVAC parts and equipment I had a contractor ask me to stop and look at a situation at an old church that was still active. The chimney liner was collapsing so the oil furnace wouldn't run. I told him to tear out the oil furnace, (It was old and in need of replacing any way) and drop in a propane 95% furnace and vent it out the wall. He called me back a few weeks later and we went back to the same church and he installed a new oil furnace and a Tjernlund side wall vent kit. Funny thing was the Tjernlund was darned near as much as the propane furnace, so it would have be a lot less money to install a 90% propane furnace. I just stood there in shock looking at what he had done. The propane furnace would need very little service where an oil burner should be looked at every year of two. Plus simpler than adding a Tjernlund sidewall vent.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,836
Location
NW Iowa
I'm not saying they are bad. I'm just not in love. Ours is pulling exhaust from a 900k gas boiler from the '70s. The chimney supposedly had a cracked clay liner so they used the tjerlund to vent through the wall.

My real complaints are install problems. The exhaust hood is too close to the air intake. We get a lot of condensation in the brick and mortar around the hood so it's not sealed well. It's definitely eating at the mortar.

I would think we could have had a stainless liner made for the chimney. It was built for an oil boiler in the '50s so I would guess there is enough room. I think I will push for that someday.

I guess I'm in charge of it now. Couldn't get anybody to diagnose the intermittent lockout problems we were having. I put a new Honeywell flame control in it and redid some things in the control cabinet.
 
OP
D
Joined
Oct 1, 2014
Messages
14
Location
NW Wisconsin
Hey Duramax Junkie. 11+ year follow up here... How did the install go if you did go thru with it? And also, if installed, how has it held up over the years?
Just happened to find this today when I googled the model number of my heater. (Forgot I even posted about it) To answer your question install went well hung it myself, a trip to Menards ran vent pipe out the roof and had the local HVAC business plumb the natural gas to it. Been going strong since haven’t had any issues with it besides at times if garage temperature is below 10F the gas valve is slow to turn on if it hasn’t ran in a couple of days
 

Mr_P

Well-known member
Joined
May 29, 2015
Messages
557
Location
Tinley Park, IL
Thank you everybody for your advice on here. Especially the original poster. I ended up with this freebie Sterling model QVF-75 built in 1996 from an estate sale where the house was going to be torn down for new housing. Now I just need to verify where I want to mount it. If I mount it right in the middle of the rear of the garage, I don't have to move too much to prep for the guy running my gas line from the basement to the garage. Most of the time I see these sitting on the corner of the garage, but unfortunately the first choice of the back left area is not accessible because of a finished room above that side of the garage.20260124_173353.jpg20260124_130423.jpg
 