Garage Heater Power

Lance101

Member
Joined
Dec 8, 2014
Messages
6
Location
Northern Indiana
Planning on putting up a natural gas unit most likely the Big Maxx or such. 45000 btu heater and was wondering how I can go about wiring it. My panel is currently full because the builder obviously cheaped out on the panel and was wondering if it would be a no no to just tap into one of the outlets in the garage. I have a gfi about 8 foot away on the wall. Not sure if a sub panel would be viable in my predicament. I'll post a picture of my box and then you can be the judge on what my best option would be. Trying to keep this the cheapest way possible. Thanks!
 

Attachments

  • image.jpg
    image.jpg
    136.8 KB · Views: 50
Last edited:
To avoid these ads, REGISTER NOW!

Jlbc212

Well-known member
Joined
Dec 7, 2013
Messages
1,530
Location
Northeast MA
You could replace the panel with one with more breaker slots. Panels are not that expensive.

The cheap way would be to run a separate line from the heater back to the panel and piggy back onto one of the breakers. Gas heaters don't draw much electricity. Use 14/2 wire and piggy back onto a 15 amp breaker.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
Do not piggy back a breaker... Replace the panel.


Sent from my iPad using Tapatalk
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
+1 to Replace Panel with larger subpanel as looks like you just have bare studs with insulation only (ie no sheetrock or wall covering yet).

You do know that GJers have lots of goodies in garage . . .
. . . 240v compressor, 240v welder, and maybe a 240v tablesaw or two . . . . ;) . . . .
. . . . you WILL need a bigger box !!! :D
 

Jarcese

Well-known member
Joined
Aug 17, 2010
Messages
194
Location
Boston, MA
How much power does it use? I can't find any electrical specs on Big Maxx or Modine. They just say 115v. I'm about to buy a Modine(which I've heard is the only way to go) and I had pretty much the same question. Will that size run on a 15 amp circuit? If so then you shouldn't bother with the panel unless you want to. The GFCI should be enough, but where are the electrical specs on these things? I'd like to know what kind of work I'm in for before I order one.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
A gas fueled unit probably only needs 15a for startup and control. They may even be able to plug into an existing outlet.


Sent from my iPad using Tapatalk
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,528
Location
Minneapolis
Gas unit heaters generally have pretty low electrical requirements (maybe 3 amps or so, depending on make, model and size) so you should be able to use the receptacle circuit for power.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,275
Location
Modesto, CA
Most breakers arent rated for 2 wires so u would either have to splice 2 wires into one to connect upto an existing breaker or tap off one of the existing outlets!
 
To avoid these ads, REGISTER NOW!

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,561
Location
Annapolis, MD
Gas unit heaters generally have pretty low electrical requirements (maybe 3 amps or so, depending on make, model and size) so you should be able to use the receptacle circuit for power.

You might be able to wire the heater with a 6' power cord (depending on the heater model) and just plug it into a receptacle. That would be your easiest option.
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR

Attachments

  • bb37412c-34fe-4005-8530-dc2532e379cd_400.jpg
    bb37412c-34fe-4005-8530-dc2532e379cd_400.jpg
    12.9 KB · Views: 24
Last edited:

Algoma56

Well-known member
Joined
Apr 16, 2007
Messages
67
Location
Sault Ste. Marie, ON
We used some mini's to get 2 breakers in one slot similar to picture above. Can't remember the actual name for them, but my electrician friend supplied and installed them. That way you can get a dedicated breaker for your heating system, which is required here.
 

Jlbc212

Well-known member
Joined
Dec 7, 2013
Messages
1,530
Location
Northeast MA
How much power does it use? I can't find any electrical specs on Big Maxx or Modine. They just say 115v. I'm about to buy a Modine(which I've heard is the only way to go) and I had pretty much the same question. Will that size run on a 15 amp circuit? If so then you shouldn't bother with the panel unless you want to. The GFCI should be enough, but where are the electrical specs on these things? I'd like to know what kind of work I'm in for before I order one.

Modine HD45 heater draws 3.7 amps according to their installation specs.
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,842
Location
NW INDIANA
I would just buy dual breaker, like shown above

No need to buy a new larger panel and rewire everything
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
I would just buy dual breaker, like shown above



No need to buy a new larger panel and rewire everything


I agree. I deal in commercial work, and didn't even know these were available...

Learn something new everyday...


Sent from my iPad using Tapatalk
 
OP
L

Lance101

Member
Joined
Dec 8, 2014
Messages
6
Location
Northern Indiana
Thanks for the replies! That additional breaker may be my best bet unless I can get away using a wall receptacle. I'm going to be building my garage at my house that I buy next year so I don't want to replace the whole box. I just need heat now for my winter garage hobbies and to keep it at around 50 when I'm not in there.
 