Please discuss. I am about to remove old K & T wiring that goes only to ceiling mounted light fixtures. Most are switched at the wall but there are 3-4 hot boxes in closets that are switched by a pull chain light fixture. Assuming I choose those fixtures to not include a receptacle, does any or all of this new work require AFCI's?
If it does, I know I can put an AFCI receptacle at the head of each circuit. I guess I would just add those in the attic. But, I'm getting ahead of the topic.
My guess is that the answer is yes, AFCI is required as per NEC 210.12(A) because of the new wording about circuits to "devices" as opposed to "outlets."
Just want to get an affirmation of this and any work-arounds such as the attic receptacles that I mentioned. I have 2 existing 15 A lighting circuits that supply a 1200 sq ft home. All the wall outlets are being rewired from the crawl space below. There are no switched receptacles anywhere.
If it does, I know I can put an AFCI receptacle at the head of each circuit. I guess I would just add those in the attic. But, I'm getting ahead of the topic.
My guess is that the answer is yes, AFCI is required as per NEC 210.12(A) because of the new wording about circuits to "devices" as opposed to "outlets."
Just want to get an affirmation of this and any work-arounds such as the attic receptacles that I mentioned. I have 2 existing 15 A lighting circuits that supply a 1200 sq ft home. All the wall outlets are being rewired from the crawl space below. There are no switched receptacles anywhere.