Im running wire to my smaller shed out back and need 30 amps there (water well and shed lights etc, nothing major.. Its 150 , and was told #10 would work fine for this.. Any comments? Thanks guys
check out this website, it lists a lot of good wiring info and references NEC 2002.
http://www.selfhelpandmore.com/home...o-dwellings/wiring-a-detached-garage-2002.php
Short story 10/3 is prob okay. You should read through the diff scenarios to be positive though.
Oh also just a thought but what's the cost per foot for 10/3 copper vs 2-2-2-4 aluminum? Here in Oklahoma it's like 1.72 a foot for the 2-2-2-4. Where as copper is outrageous. I was thinking about running 6/3 to my shed for 60 amps and then I noticed it was around $3.50 a foot.
Don't know where you are buying your wire, but I bought some 6/3 a couple days ago and it was $1.45/ft. 6 guage is only rated to 55 amps BTW.
Well it's one of those deals where if I buy a 500' spool it's 50% off. But I've never needed 500'.
alot of time, if you need 200 or 300ft, its cheapest to buy the spool, use what you need and sell the rest.
If I was doing this job, i would look into the cost of runnning pvc conduit and buying a 500ft spool of #8.
Well, lets look at that -3/4in sch40 pvc conduit = $1.80 a stick, so $27 plus fittings so call it $40, plus $117 for a 500ft roll of #8 THHN. So $157 for the whole thing, #8 copper in PVC conduit, so $1.04 per foot. Not bad.
Oops, i screwed up you need a little over 600ft of wire. So buy a spool of 500ft #10 for $90 and sell the leftover 8 and the 350ft spool of 10, or buy #10 by the foot, and you still come out pretty good in the end.
Problem is, conductors of #6 or smaller cannot be remarked on the ends to distinguish the neutral (grounded conductor) NEC 200.6(A) .......... and NEC 200.7(C) doesn't allow the use of a remarked white wire as a hot, unless it is in a "cable" (such as Romex)...... So you would have to buy spools of white and black, both.
Charles
Thanks , that's what I was thinking.. Yes , we plan on using 1" PVC and the wiring will be underground rated as well. Was digging yesterday and found my old old septic lines, and they were full of ground water,great, what a mess now... Thanks guy for the info.Paul