Im running wire to my smaller shed out back and need 30 amps there (water well and shed lights etc, nothing major.. Its 150 , and was told #10 would work fine for this.. Any comments? Thanks guys
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
150ft away? What is the FLA of the motor on the well pump? I think youre going to need larger than #10, probably 8, maybe even 6.
 

structures282

Active member
Joined
Mar 19, 2009
Messages
44
Location
Oklahoma
check out this website, it lists a lot of good wiring info and references NEC 2002.

http://www.selfhelpandmore.com/home...o-dwellings/wiring-a-detached-garage-2002.php

Short story 10/3 is prob okay. You should read through the diff scenarios to be positive though.

Oh also just a thought but what's the cost per foot for 10/3 copper vs 2-2-2-4 aluminum? Here in Oklahoma it's like 1.72 a foot for the 2-2-2-4. Where as copper is outrageous. I was thinking about running 6/3 to my shed for 60 amps and then I noticed it was around $3.50 a foot.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Yes, the alum is a bargain and what we use on long circuits. I mostly use a 60 breaker on them but like the 90A wire, at 200 ft I think it is still near 2% V drop at 50A. Up sized wire is a great asset for motor starts and you can weld from it should the need arise.
 
OP
P

paul2112

Well-known member
Joined
Feb 15, 2009
Messages
258
Location
Waxahachie,TX
Its just a 220v 3/4 hp motor 6amp. The only other thing i use out there is my lights , drills small tools etc.Thanks guys
 

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Don't know where you are buying your wire, but I bought some 6/3 a couple days ago and it was $1.45/ft. 6 guage is only rated to 55 amps BTW.

check out this website, it lists a lot of good wiring info and references NEC 2002.

http://www.selfhelpandmore.com/home...o-dwellings/wiring-a-detached-garage-2002.php

Short story 10/3 is prob okay. You should read through the diff scenarios to be positive though.

Oh also just a thought but what's the cost per foot for 10/3 copper vs 2-2-2-4 aluminum? Here in Oklahoma it's like 1.72 a foot for the 2-2-2-4. Where as copper is outrageous. I was thinking about running 6/3 to my shed for 60 amps and then I noticed it was around $3.50 a foot.
 
To avoid these ads, REGISTER NOW!

structures282

Active member
Joined
Mar 19, 2009
Messages
44
Location
Oklahoma
Don't know where you are buying your wire, but I bought some 6/3 a couple days ago and it was $1.45/ft. 6 guage is only rated to 55 amps BTW.

Well it's one of those deals where if I buy a 500' spool it's 50% off. But I've never needed 500'.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Well it's one of those deals where if I buy a 500' spool it's 50% off. But I've never needed 500'.

alot of time, if you need 200 or 300ft, its cheapest to buy the spool, use what you need and sell the rest.

If I was doing this job, i would look into the cost of runnning pvc conduit and buying a 500ft spool of #8.

Well, lets look at that -3/4in sch40 pvc conduit = $1.80 a stick, so $27 plus fittings so call it $40, plus $117 for a 500ft roll of #8 THHN. So $157 for the whole thing, #8 copper in PVC conduit, so $1.04 per foot. Not bad.

Oops, i screwed up you need a little over 600ft of wire. So buy a spool of 500ft #10 for $90 and sell the leftover 8 and the 350ft spool of 10, or buy #10 by the foot, and you still come out pretty good in the end.
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
alot of time, if you need 200 or 300ft, its cheapest to buy the spool, use what you need and sell the rest.

If I was doing this job, i would look into the cost of runnning pvc conduit and buying a 500ft spool of #8.

Well, lets look at that -3/4in sch40 pvc conduit = $1.80 a stick, so $27 plus fittings so call it $40, plus $117 for a 500ft roll of #8 THHN. So $157 for the whole thing, #8 copper in PVC conduit, so $1.04 per foot. Not bad.

Oops, i screwed up you need a little over 600ft of wire. So buy a spool of 500ft #10 for $90 and sell the leftover 8 and the 350ft spool of 10, or buy #10 by the foot, and you still come out pretty good in the end.

Problem is, conductors of #6 or smaller cannot be remarked on the ends to distinguish the neutral (grounded conductor) NEC 200.6(A) .......... and NEC 200.7(C) doesn't allow the use of a remarked white wire as a hot, unless it is in a "cable" (such as Romex)...... So you would have to buy spools of white and black, both.

Charles
 

BoydS

Well-known member
Joined
Apr 28, 2007
Messages
184
Location
South of Houston
Paul ... for service to the shed that only will supply power for a 6 amp (220V) water well pump, light (lets say 200 watts) and one receptacle for power tools (receptacle at 180 watts) the #10 would work just fine. This is assumed the feeder would be installed in PCV conduit underground. With a 150 foot run voltage drop (3%) needs to be consided and a #10 would work just fine in this situation.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Problem is, conductors of #6 or smaller cannot be remarked on the ends to distinguish the neutral (grounded conductor) NEC 200.6(A) .......... and NEC 200.7(C) doesn't allow the use of a remarked white wire as a hot, unless it is in a "cable" (such as Romex)...... So you would have to buy spools of white and black, both.

Charles

oh yeah, forgot about that. I still vote for PVC in the ground vs cable.
 
OP
P

paul2112

Well-known member
Joined
Feb 15, 2009
Messages
258
Location
Waxahachie,TX
Thanks , that's what I was thinking.. Yes , we plan on using 1" PVC and the wiring will be underground rated as well. Was digging yesterday and found my old old septic lines, and they were full of ground water,great, what a mess now... Thanks guy for the info.Paul
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Thanks , that's what I was thinking.. Yes , we plan on using 1" PVC and the wiring will be underground rated as well. Was digging yesterday and found my old old septic lines, and they were full of ground water,great, what a mess now... Thanks guy for the info.Paul

if youre running it in conduit, you dont need to (nor do you want to) use any sort of cable or 'underground' wire. The wire just needs to be listed for wet location (all underground conduits are considered a wet location) which all THHN/THWN is. So you just need normal wire.
 