Is this a main panel or a sub panel? The conventions are different for each.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The wire needs to be one continuous piece from panel to the rods. You can get the wire to the panel how ever you want as long as it's not in a place that it can get damaged. If running across the ground where a shovel may get it the wire needs to be placed in a sleeve of EMT or copper water pipe. As far as getting it in the house, for an example you can strap it to the side of the meter conduit coming up from the ground and bore a small hole in the house wall and push it inside. You can bore a small hole in the foundation and push it though to under the crawl space and bring it up to the panel.
 

_Dock_

Well-known member
Joined
Jan 10, 2011
Messages
169
Location
Ky
Patten p put you in the right direction. One thing to remember if you a running conduit from your main to your sub the ground wire cannot run in any part if the conduit with your conductors.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
The wire needs to be one continuous piece from panel to the rods. You can get the wire to the panel how ever you want as long as it's not in a place that it can get damaged. If running across the ground where a shovel may get it the wire needs to be placed in a sleeve of EMT or copper water pipe. As far as getting it in the house, for an example you can strap it to the side of the meter conduit coming up from the ground and bore a small hole in the house wall and push it inside. You can bore a small hole in the foundation and push it though to under the crawl space and bring it up to the panel.

I believe once the continuous wire is properly clamped to the closest rod you can connect the 2 rods with another ground and set of approved clamps. Here are 2 drawings of different scenarios. Ignore the 'existing' ground wire.

45587d1328819604-multiple-ground-rods-help-scan_pic0001a.jpg


45647d1328901232-multiple-ground-rods-help-scan_pic0001b.jpg


No, I didn't draw those. ;)
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
If running across the ground where a shovel may get it the wire needs to be placed in a sleeve of EMT or copper water pipe.

And if it EMT or Rigid Conduit, you will need to bond it on both ends . If you don't the choking effect that ungrounded ferrous conduit has will greatly reduce the ground wire's effectiveness.

And the NEC requires it

You could always go with Schedule 80PVC
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Don't know your local codes but in nj you can run the thhn right out of ground and into back of panel or into foundation and then into panel. Never have or have seen any house that put the ground rod wire into a pipe or sleeve.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Don't know your local codes but in nj you can run the thhn right out of ground and into back of panel or into foundation and then into panel. Never have or have seen any house that put the ground rod wire into a pipe or sleeve.



THHN? Huh? Usually solid bare cu #6 or #8 is used...
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If thinner than #6 solid I seem to recall that it is required to be protected where exposed.

As far as entering the panel, most panels have a tiny knockout, about ¼" in the back corner of the bottom and top of the housing. You take a small punch and knock it out, and run the ground thru it.

Charles
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
If thinner than #6 solid I seem to recall that it is required to be protected where exposed.

As far as entering the panel, most panels have a tiny knockout, about ¼" in the back corner of the bottom and top of the housing. You take a small punch and knock it out, and run the ground thru it.

Charles

Yes thinner than #6 is required to be in conduit. And if the #6 is in an area where it can get damaged then it needs to be in conduit as well!!
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Yes thinner than #6 is required to be in conduit. And if the #6 is in an area where it can get damaged then it needs to be in conduit as well!!

Must be a west coast thing because it's not required here or if it is it's not enforced, I've done 100+ services and seen a lot and none had the ground wire in pipe outside the house, not that it couldn't hurt just not done here
 
To avoid these ads, REGISTER NOW!

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
That's why I always just run #4 bare cu, because under that size is required to be protected. The price increase is minimal and you don't have to mess with conduit, and bonding if metal as has been mentioned.

Now that I think of it, I don't recall anything in NEC that specifies solid for this use, but that's what I've always used and seem to recall inspectors always wanted to see. But THHN is probably fine if that's the case. It would have to be green insulation.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
Now that I think of it, I don't recall anything in NEC that specifies solid for this use, but that's what I've always used and seem to recall inspectors always wanted to see. But THHN is probably fine if that's the case. It would have to be green insulation.

The Code doesn't specify solid or stranded. You'd have a hard time installing solid 2/0 or 3/0 Grounding Electrode Conductor, even if it was available (I think the biggest produced is #2 solid). THWN is commonly used as a GEC.

The GEC doesn't need to be green. No color is required. You could use Black or even Pink if that is what you desire.

The requirement for conduit isn't just a "West Coast" thing. It's required in the NEC where the GEC is subject to physical damage.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
And if it EMT or Rigid Conduit, you will need to bond it on both ends . If you don't the choking effect that ungrounded ferrous conduit has will greatly reduce the ground wire's effectiveness.

And the NEC requires it

You could always go with Schedule 80PVC

Will you please state the NEC section that says a metal protective sleeve on the grounding electrode conductor has to be bonded to the electrode conductor.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Will you please state the NEC section that says a metal protective sleeve on the grounding electrode conductor has to be bonded to the electrode conductor.
I'm not sure yet where it is in the NEC, but I do agree, yes, it MUST be bonded.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
250.64 (E)
Enclosures for Grounding Electrode Conductor.

Ferrous (iron/steel) raceways, boxes, and enclosures containing the grounding electrode conductors must be made electrically continuous by bonding each end of the ferrous metal raceway, box, and enclosure to the grounding electrode conductor.

That's from a previous Edition of the Code.......It still says pretty much the same thing, though, with a lot more text

From the 2011 NEC
Bonding methods in compliance with 250.92(B) for installations at service equipment locations and with 250.92(B)(2) through (B)(4) for other than service equipment locations shall apply at each end and to all intervening ferrous raceways, boxes, and enclosures between the cabinets or equipment and the grounding electrode
 
Last edited:

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
The Code doesn't specify solid or stranded. You'd have a hard time installing solid 2/0 or 3/0 Grounding Electrode Conductor, evenrce if it was available (I think the biggest produced is #2 solid). THWN is commonly used as a GEC.

The GEC doesn't need to be green. No color is required. You could use Black or even Pink if that is what you desire.

The requirement for conduit isn't just a "West Coast" thing. It's required in the NEC where the GEC is subject to physical damage.

Well it's a good thing none of the inspectors enforce in nj, waste of time and money
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'm just talking about short sleeve buried outside for protection. I'don't think it's necessary by code to bond. At least not here.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,595
Location
Fullerton, CA
Gleaned from the Mike Holt website:

CAUTION: The effectiveness of the grounding electrode can be significantly reduced if a ferromagnetic raceway containing a grounding electrode conductor isn't bonded to the grounding electrode conductor at both ends. This is because a single conductor carrying high-frequency lightning current in a ferrous raceway causes the raceway to act as an inductor, which severely limits (chokes) the current flow through the grounding electrode conductor. ANSI/IEEE 142, Recommended Practice for Grounding of Industrial and Commercial Power Systems (Green Book) states, "An inductive choke can reduce the current flow by 97 percent."

From ECM:
Section 250.64(E) requires ferrous metal enclosures for grounding electrode conductors that are not physically continuous from cabinets or equipment to the grounding electrode, such as sleeves or short lengths of conduit used for physical protection, to be made electrically continuous by bonding each end of the raceway to the contained grounding electrode conductor.

Just use PVC 80 It's nonmagnetic and doesn't need to bonded:)
 
Last edited:

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Here is South Jersey they require ground rods and Upher grounds,which is continuous ground through rebar and mesh infloor to the panel

Yeah but when you come out of the ground and up the outside of the house a foot or two before going into the house,do you sleeve it inside pipe. I have never seen it on a residential house or put one in. In fact I just did a generator where the wire from the ground rods came out of ground and right into transfer switch. No pipe, just need to secure it so it's not loose.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Well it's a good thing none of the inspectors enforce in nj, waste of time and money
I was called on it once, many years ago. I was pretty close with the inspector, and when he explained it to me it made complete sense. He said he had seen the end of a pipe sleeve literally blow apart from a lightning hit, where if it were bonded it would not have.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
We talking two different things, I was talking about not having a pipe at all and just the wire running up the foundation, your talking if you have a pipe and not connecting the ends where I could see that happening like you mentioned
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
My understanding and what i was taught is #6 can be ran by itself without sleeve or conduit, unless subject to damage. Smaller than #6 always needs to be in sleeve/conduit...2011 book is at the shop so ill have to look when i get back...

Ive seen many GECs sleeved in EMT right upto the rod....
 