Hi, This is a long first post. I have been reading threads for days on this site about these topics but thought I would reach out.
I built a 24'x30' detached garage with the following specs:
6" slab with 12" thickened edge. R-10 rigid pink foam around the perimeter and R-8 ISORAD foam under the pad. This is the foam with groves the Pex sits into. Expensive but very easy to use. There is a thick poly barrier under all the foam and pipes.
720 sq ft.
2x6 Wood framed walls with R-20 batts. R-50 in the ceiling.
2- 9'x8' T16 overhead door -R-16. -144 sq ft
1- 36"x80" insulated steel entry door. - 24 sq ft
3- 2'x5' PVC double pane windows. - 30 sq ft
Per local building codes there is 6mil poly vapor barrier on walls and ceiling. Everything is sealed with Acoustical sealant.
3 Loop PEX system with equal length for all 3 loops. 240' per loop
The garage is built to and exceeds some local standards. The building inspector actually told me he wished the large home builders in the area put as much effort into the houses they build as I did for the garage.
In Manitoba it can get down to -35C (-31F) during the winter. On the coldest of cold days I would like the garage to maintain a temperature of about 15C (60F). So about a 90F rise above the coldest outside temp. If I don't plan on being in the garage working on something the temp could be turned down to 7-10C (45-50), 75F rise.
Now to the problems and second part of the thread title.
Has to be an electric boiler. Electricity is about $0.07/kWh. The electrical in the garage is already done. It has a sub panel that is connected to my home 100amp service from a 60amp breaker fed by new #6 copper wire.
Some local supply companies say that a 6kw (20,473btu) boiler will be adequate for my goals and some say I would need a 8kw (27,297btu).
Here is a link to the boiler company I will be going with.
http://www.conceptmfginc.com/leb.html
Both cost the same, but my electrician said I wouldn't be able to run a 8kw boiler with the electrical service I have in the house/garage. He said with a 6kw boiler I would be able to run other larger devices in the garage at the same time, but anything larger than a 6kw and I wouldn't be able to run much more than just the lighting.
Now back to the first part of the thread title.
I have used some online heat loss calculators and have got wildly varying results. Anywhere from 13,500btu - 22,000btu. I really just don't know enough about them to use and understand them properly.
What has me worried is that a friend built a 832 sq ft garage that is almost the same as mine in size, materials used, and construction methods. He had a heat loss calculation done and his came in at 29,303btu. That included 14,319btu for infiltration. He put a 6kw boiler in his garage and can't get the temp past 10C (50F). He is upgrading to a 9kw boiler (30,000btu) hoping that will get the temps inside up.
Is there anyone in similar cold climates that have a similar sized garage and floor setup that have real world results with boiler sizing and heat loss?
TL;DR Will a 6kw boiler be able to produce enough heat to keep the garage near room temp in the middle of winter if necessary?
I built a 24'x30' detached garage with the following specs:
6" slab with 12" thickened edge. R-10 rigid pink foam around the perimeter and R-8 ISORAD foam under the pad. This is the foam with groves the Pex sits into. Expensive but very easy to use. There is a thick poly barrier under all the foam and pipes.
720 sq ft.
2x6 Wood framed walls with R-20 batts. R-50 in the ceiling.
2- 9'x8' T16 overhead door -R-16. -144 sq ft
1- 36"x80" insulated steel entry door. - 24 sq ft
3- 2'x5' PVC double pane windows. - 30 sq ft
Per local building codes there is 6mil poly vapor barrier on walls and ceiling. Everything is sealed with Acoustical sealant.
3 Loop PEX system with equal length for all 3 loops. 240' per loop
The garage is built to and exceeds some local standards. The building inspector actually told me he wished the large home builders in the area put as much effort into the houses they build as I did for the garage.
In Manitoba it can get down to -35C (-31F) during the winter. On the coldest of cold days I would like the garage to maintain a temperature of about 15C (60F). So about a 90F rise above the coldest outside temp. If I don't plan on being in the garage working on something the temp could be turned down to 7-10C (45-50), 75F rise.
Now to the problems and second part of the thread title.
Has to be an electric boiler. Electricity is about $0.07/kWh. The electrical in the garage is already done. It has a sub panel that is connected to my home 100amp service from a 60amp breaker fed by new #6 copper wire.
Some local supply companies say that a 6kw (20,473btu) boiler will be adequate for my goals and some say I would need a 8kw (27,297btu).
Here is a link to the boiler company I will be going with.
http://www.conceptmfginc.com/leb.html
Both cost the same, but my electrician said I wouldn't be able to run a 8kw boiler with the electrical service I have in the house/garage. He said with a 6kw boiler I would be able to run other larger devices in the garage at the same time, but anything larger than a 6kw and I wouldn't be able to run much more than just the lighting.
Now back to the first part of the thread title.
I have used some online heat loss calculators and have got wildly varying results. Anywhere from 13,500btu - 22,000btu. I really just don't know enough about them to use and understand them properly.
What has me worried is that a friend built a 832 sq ft garage that is almost the same as mine in size, materials used, and construction methods. He had a heat loss calculation done and his came in at 29,303btu. That included 14,319btu for infiltration. He put a 6kw boiler in his garage and can't get the temp past 10C (50F). He is upgrading to a 9kw boiler (30,000btu) hoping that will get the temps inside up.
Is there anyone in similar cold climates that have a similar sized garage and floor setup that have real world results with boiler sizing and heat loss?
TL;DR Will a 6kw boiler be able to produce enough heat to keep the garage near room temp in the middle of winter if necessary?