Easiest way to wire this?

robertwhite

Well-known member
Joined
Feb 10, 2010
Messages
433
Sorry for the crude drawing....

Want to use ONE circuit (20A breaker) to wire 2 independent can lights, each with their own switch.

All areas are accessible.

This would be simple if both switches were in the same gang box, but these switches will be at either end of a 20 ft room where a wall will be. The wall in between makes the 2 areas separate, and each room has its own purpose.

Looking for the easiest way to do this with 12/2 or 12/3 wire (I only want to use one breaker slot in the panel)
 

Attachments

  • can light.jpg
    can light.jpg
    29.5 KB · Views: 98
To avoid these ads, REGISTER NOW!

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
Sorry for the crude drawing....

Want to use ONE circuit (20A breaker) to wire 2 independent can lights, each with their own switch.

All areas are accessible.

This would be simple if both switches were in the same gang box, but these switches will be at either end of a 20 ft room where a wall will be. The wall in between makes the 2 areas separate, and each room has its own purpose.

Looking for the easiest way to do this with 12/2 or 12/3 wire (I only want to use one breaker slot in the panel)

Go from the panel to switch 1 with your 12/2, on your switch you will have a plug in lug and a push in {std on most 20a switches}, L1 will go into the puch in of the switch, then run the 12/2 to the light that switch operates. Now also run a 12/2 from that box {use the screw lug} to the switch box for light 2... Easy enough, you are using switch 1 as a junction box for switch 2.

Switch 1 switches light one but the hot side of the switch also feeds switch 2. You can use a larger box for this and use wire nuts, but for something like this the push in connector is how I would do it, I hate using them but I also hate a bunch of wire nuts everywhere...
 

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
12/2 from Panel to first switch. 12/2 from first switch to second switch. 12/2 from switch one to light one. 12/2 from switch two to light two. In the switch box you will have a feed in feed out and load to the light. All grounds together. All whites together. 1 black to the light stays by itself. The other blacks splice and pigtail.
 

n8n

Well-known member
Joined
Mar 11, 2014
Messages
3,613
Location
Curtis Bay, MD
^that. but pull 12/3 for the switch legs as current code requires a neutral be present at the switch even if not used.
 

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
If all areas are accessible utilizing 3 wire and switch legs is a waste and completely unnecessary.
 

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,638
Location
Lubbock TX
12/2 from Panel to first switch. 12/2 from first switch to second switch. 12/2 from switch one to light one. 12/2 from switch two to light two. In the switch box you will have a feed in feed out and load to the light. All grounds together. All whites together. 1 black to the light stays by itself. The other blacks splice and pigtail.

Agreed. This would be my approach.

DC
 
OP
R

robertwhite

Well-known member
Joined
Feb 10, 2010
Messages
433
12/2 from Panel to first switch. 12/2 from first switch to second switch. 12/2 from switch one to light one. 12/2 from switch two to light two. In the switch box you will have a feed in feed out and load to the light. All grounds together. All whites together. 1 black to the light stays by itself. The other blacks splice and pigtail.

So if I understand this correctly, this set up is doing the same thing as would be done if the switches were in the same gang box, (pulling power, then splitting to each switch) just at a longer distance, yes?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
Go from the panel to switch 1 with your 12/2, on your switch you will have a plug in lug and a push in {std on most 20a switches}, L1 will go into the puch in of the switch, then run the 12/2 to the light that switch operates. Now also run a 12/2 from that box {use the screw lug} to the switch box for light 2... Easy enough, you are using switch 1 as a junction box for switch 2.

Switch 1 switches light one but the hot side of the switch also feeds switch 2. You can use a larger box for this and use wire nuts, but for something like this the push in connector is how I would do it, I hate using them but I also hate a bunch of wire nuts everywhere...

dont use the backwire push in backstabs. Horrible idea. They WILL fail and stab u in the back!(pun intended) :lol: Use a wire nut and pig tails!
 
To avoid these ads, REGISTER NOW!

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,475
Location
AZ
^that. but pull 12/3 for the switch legs as current code requires a neutral be present at the switch even if not used.

Say what?. Granted I don't even remotely stay up with resi code, but please site that code section, I got to see this with my own eyes. Thanks
 

djnigel

New member
Joined
Sep 14, 2014
Messages
1
frist of i am a electrician and i would run a 14-2 hr to the 1st switch and run a 14-3 to the other and then a 14-2 to the lights if you need help wiring the switches let me know
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
frist of i am a electrician and i would run a 14-2 hr to the 1st switch and run a 14-3 to the other and then a 14-2 to the lights if you need help wiring the switches let me know
Again ,with the wall open there is NO need for 3-wire.

Though I would also use #14 on a 15A. Absolutely NO reason for #12 for this circuit.
 