Can dimmer's break wires?

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
About a year ago, all of the "can" lights in my bedroom started flashing on and off (they are controlled by a 3 way electronic dimmer). Called an electrician and he found a broken wire from the attic down to the switch by using a meter with a ringer.We replaced the wire and all was fine for about a year, until last night when these same lights started flashing off and on again. I am now wondering if the dimmer might be causing the problem. Any thoughts??
 
To avoid these ads, REGISTER NOW!

Caman

Well-known member
Joined
Feb 1, 2015
Messages
486
Location
MN
Mice, squirrels, rats, raccoons...all possible suspects.
 

Redwolf947

Well-known member
Joined
Feb 13, 2015
Messages
613
Location
South East WI
About a year ago, all of the "can" lights in my bedroom started flashing on and off (they are controlled by a 3 way electronic dimmer). Called an electrician and he found a broken wire from the attic down to the switch by using a meter with a ringer.We replaced the wire and all was fine for about a year, until last night when these same lights started flashing off and on again. I am now wondering if the dimmer might be causing the problem. Any thoughts??

I guess we should ask in what way was the first wire broken?
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Are the "can" lights over heating, causing the temperture switch to trip, reset trip again ???????

First thing I think when "can" lights flash .......Over heating as too large of bulb, not IC approved fixture ..........this theory does not check with prior repair.
 
Last edited:
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
No, not mice, rats or squirrels, and not an overheat condition (I don't believe), as they start flashing almost immediately after turn on. The reason I say it's not animals is because one lead of the cable inside of the jacket was broken, the jacket was not damaged. The electrician told me that possibly vibration more than likely broke the wire. He stated that alternating current could cause a vibration which may have broken the wire( it was 25 years old). The new wire is less than a year old. My thought was that possibly the dimmer, which is about 2 years old was somehow setting up a vibration.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
I cant explain a broken wire, but the flashing might be incompatibility between dimmer and lamp. CFL's are the worst thing to try to dim, and LED's are no picnic either. Flashing lights can be a common symptom.
Good luck
CD
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
I don't understand how a wire can just arbitrarily break inside the sheathing. Wires are run thru walls all the time and they don't break. I could maybe understand the vibration thing breaking a wire if the wire was connected to a ceiling fan that was out of balance and was shaking, but other than that something doesn't sound quite right to me.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Wires just don't break inside the jacket,either another issue or old wire was messed up in the first place. Could be staple to tight also
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
I cant explain a broken wire, but the flashing might be incompatibility between dimmer and lamp. CFL's are the worst thing to try to dim, and LED's are no picnic either. Flashing lights can be a common symptom.
Good luck
CD

I don't understand how a wire can just arbitrarily break inside the sheathing. Wires are run thru walls all the time and they don't break. I could maybe understand the vibration thing breaking a wire if the wire was connected to a ceiling fan that was out of balance and was shaking, but other than that something doesn't sound quite right to me.

Actually these are just incandescent flood's, and mostly original bulbs from 20 years ago. The lights are only on for a few minutes at night, and almost always in a dimmed state. I changed the dimmers about 2 years ago from old mechanical one's to an electronic model. Never had a problem until a year later, and now another year after replacing the original wire (although I don't know for sure that it is a broken wire this time, but it's the same symptoms).
 

n8n

Well-known member
Joined
Mar 11, 2014
Messages
3,607
Location
Curtis Bay, MD
Dimmers can generate heat, if it is old wire it can cause the insulation to fail. I don't see how the wire would physically break though unless the dimmer was actually vibrating (possible, can you hear any noise from it?)
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Dimmers can generate heat, if it is old wire it can cause the insulation to fail. I don't see how the wire would physically break though unless the dimmer was actually vibrating (possible, can you hear any noise from it?)

I just put a stethoscope to both dimmers and although the lights were flashing, there was no noise.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
No, not mice, rats or squirrels, and not an overheat condition (I don't believe), as they start flashing almost immediately after turn on. The reason I say it's not animals is because one lead of the cable inside of the jacket was broken, the jacket was not damaged. The electrician told me that possibly vibration more than likely broke the wire. He stated that alternating current could cause a vibration which may have broken the wire( it was 25 years old). The new wire is less than a year old. My thought was that possibly the dimmer, which is about 2 years old was somehow setting up a vibration.

now that my friend is a load of monkeypoo! :monkey_po

Yes AC current causes hum, which can in turn cause vibration but this is only present in transformers where high magnetic fields are present. Have u ever tried to break a 14ga or 12ga wire by vibrating it? It doesnt work. U have to bend the wire back and forth several times to get it to snap. And broken inside the jacket? Do U realize that NM wire is tightly packed inside its jacket? 25 yr old NM-b wire is not that old! Never seen this before ever. And Ive done tons of service calls...
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
now that my friend is a load of monkeypoo! :monkey_po

Yes AC current causes hum, which can in turn cause vibration but this is only present in transformers where high magnetic fields are present. Have u ever tried to break a 14ga or 12ga wire by vibrating it? It doesnt work. U have to bend the wire back and forth several times to get it to snap. And broken inside the jacket? Do U realize that NM wire is tightly packed inside its jacket? 25 yr old NM-b wire is not that old! Never seen this before ever. And Ive done tons of service calls...

Well, at the time, I thought he was just giving some kind of BS answer, so he could get on to his next job, but when it happened again I began to wonder.
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Just an update, as I don't like to leave this kind of thread hanging, no one learn's if you do.
I poked around a little this morning and found a loose ground wire at the dimmer where he replaced the wire. Reconnected the ground and all seems to be good. Thanks for all the thoughts !!
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Just an update, as I don't like to leave this kind of thread hanging, no one learn's if you do.
I poked around a little this morning and found a loose ground wire at the dimmer where he replaced the wire. Reconnected the ground and all seems to be good. Thanks for all the thoughts !!

Glad you fixed it but not in the way you describe. The GROUND (bare wire) should not be in play here. It causing the lights to blink indicates it is a current carrying conductor and that is not right. Perhaps you tightened or fixed a loose neutral or hot wire while you were at it which will explain the issue. Is this dimmer some sort of SMART dimmer per chance? Some very small amount of sneak current is (was) allowed, (0.5ma), via GROUND.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Glad you fixed it but not in the way you describe. The GROUND (bare wire) should not be in play here. It causing the lights to blink indicates it is a current carrying conductor and that is not right. Perhaps you tightened or fixed a loose neutral or hot wire while you were at it which will explain the issue. Is this dimmer some sort of SMART dimmer per chance? Some very small amount of sneak current is (was) allowed, (0.5ma), via GROUND.

Yes please dont use the ground as a current carrying conductor. Total hack work... :shocking:
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Well, maybe it isn't fixed then, although the lights didn't flash after I found the loose ground. Looks like I need to explore a little more. I did tighten all of the wire nuts while I was in the box, but the ground was the only one that pulled out when I tugged on it. I have a meter, so I'll check to see if the ground is hot and report back. As you can tell, I'm white to white, black to black and ground to ground type of guy.If it gets much more complicated than that, I normally call an electrician.
 
To avoid these ads, REGISTER NOW!

n8n

Well-known member
Joined
Mar 11, 2014
Messages
3,607
Location
Curtis Bay, MD
Well, *is* it a "smart" dimmer, and was a non-bare or green wire connected from the dimmer to the ground bundle?
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Just checked the ground, nothing going thru it, I'll leave the lights on the rest of the day and see if they start flashing again.
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Well, *is* it a "smart" dimmer, and was a non-bare or green wire connected from the dimmer to the ground bundle?

How did u check to see that "nothing was going through it?" A current clamp i hope...

No, not a smart dimmer, and yes the green wire was(or maybe I should say, is now) connected to the ground bundle.

Actually I used a Greenlee GT-11 Voltage detector. It is super sensitive, static will set it off. Then I pulled the nut off and put my finger on the ground bundle. Pretty sure it's not hot.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
No, not a smart dimmer, and yes the green wire was(or maybe I should say, is now) connected to the ground bundle.

Actually I used a Greenlee GT-11 Voltage detector. It is super sensitive, static will set it off. Then I pulled the nut off and put my finger on the ground bundle. Pretty sure it's not hot.

Thats not gonna tell u if current is flowing through the ground because u didnt complete a circuit and youre already at the same potential as ground...u would need a current clamp to check...
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
Look, this is all so silly, missing SO many pertinent details.

Too tired for a step by step post, I'm a verrrryyy slow typer, so will just say GET A NEW ELECTRICIAN THAT AT LEAST UNDERSTANDS THEORY 101.

Where the heck is the "eating popcorn" emoticon when I need it. Marc
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
Aye Aye Aye- The cans may INDIVIDUALLY go on/ off if conditions are not right.
Noone ever said/ or asked, if ALL are going off simultaneously OR independantly.

OMG.
Among other left out details. YARRRRRRR Marc
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Aye Aye Aye- The cans may INDIVIDUALLY go on/ off if conditions are not right.
Noone ever said/ or asked, if ALL are going off simultaneously OR independantly.

OMG.
Among other left out details. YARRRRRRR Marc

Ummm...ahem the OP said in the first post that they ALL started going on and off!
 
OP
J

jannan

Well-known member
Joined
Apr 20, 2013
Messages
52
Thanks for all the thoughts guys. Problem seems to be solved. Probably a loose wire in the box, definately a loose ground. As suggested, if the problem arises again I'll get a different electrician. Obviously this guy did sloppy work.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Just a guess, the problem could have been the dimmer. The loose ground I spose could have made it do that, as dimmers with no neutral connection need a ground connection to send milliamps back to earth. Hence the need for a neutral at a switch box. But different topic altogether.
You will have current on your ground from your dimmer, but it is considered acceptable and it is by design, again only milliamps.
 

abk241

Well-known member
Joined
Aug 22, 2014
Messages
310
Location
SF Bay Area, California
No, not mice, rats or squirrels, and not an overheat condition (I don't believe), as they start flashing almost immediately after turn on. The reason I say it's not animals is because one lead of the cable inside of the jacket was broken, the jacket was not damaged. The electrician told me that possibly vibration more than likely broke the wire. He stated that alternating current could cause a vibration which may have broken the wire( it was 25 years old). The new wire is less than a year old. My thought was that possibly the dimmer, which is about 2 years old was somehow setting up a vibration.

60 cycle hum as the cause of broken wires???
That's a new one for me.
 