Receptacle Requirement

Al G

Well-known member
Joined
Jan 5, 2015
Messages
340
Location
Arizona
A house question - I had a concealment inspection on my basement yesterday. The inspector asked what I was going to do with a 4" steel column. I told we were either going to buy a prefab column cover or box it in with 1x after drywall and floor. We want to keep it as small as possible. He said if the total measurement around the column exceeds 24" an outlet is required. I asked to clarify thinking maybe he meant 24" on any side. He said 24" total. Thus a 6x6x6x6 column would require an outlet. I didn't push him for a reference yet because I don't want to make an enemy of him. I think I can stay under 24" but has anyone heard of this requirement before? It just doesn't make sense to me.
 
To avoid these ads, REGISTER NOW!

Morrison

Well-known member
Joined
Dec 15, 2013
Messages
1,195
Location
Northeast
You can probably stay under his 24" rule. If not leave the beam alone till after his final inspection, then cover it how every you want.
 
Last edited:

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
The code is that any wall space longer than 24 in in the horizontal must have a receptacle. In this case if the column is round and more than 24 in circumference then the inspector is correct. With a square column i would have to look closer at the code and see what it says. If there is a receptacle within 6ft of the column he may let you slide on this. What edition of the code is your area using?
 
Last edited:

Tdubyac

Well-known member
Joined
May 10, 2014
Messages
63
Location
Chapel Hill, NC
There is a requirement for an outlet on any wall wider then 2 feet in length. I would do like Morrison suggested and just leave it alone until after inspection.
 
OP
A

Al G

Well-known member
Joined
Jan 5, 2015
Messages
340
Location
Arizona
The code is that any wall space longer than 24 in in the horizontal must have a receptacle. In this case if the column is round and more than 24 in circumference then the inspector is correct. With a square column i would have to look closer at the code and see what it says. If there is a receptacle within 6ft of the column he may let you slide on this. What edition of the code is your area using?

I knew about the 24" requirement but thought that meant a single surface. I can put a table against a 24" wall. I can't put a table against a 24" circumference.

I believe we are on the 2011 code. I know it is not the 2014 code.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
While yes, this is the letter of the code, for him to enforce requiring a receptacle on a 6x6x6x6 column is ABSURD! It definitely could be argued that this is not "wall" space since wall spaces are clearly defined in the code.
I wouldn't call a column a fixed panel, a railing or room divider.

210.52(A)(2) Wall Space.

As used in this section, a wall space shall include the following:

(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets

(2) The space occupied by fixed panels in exterior walls, excluding sliding panels

(3) The space afforded by fixed room dividers, such as freestanding bar-type counters or railings
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
While yes, this is the letter of the code, for him to enforce requiring a receptacle on a 6x6x6x6 column is ABSURD! It definitely could be argued that this is not "wall" space since wall spaces are clearly defined in the code.
I wouldn't call a column a fixed panel, a railing or room divider.

Quote:
210.52(A)(2) Wall Space.

As used in this section, a wall space shall include the following:

(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets

(2) The space occupied by fixed panels in exterior walls, excluding sliding panels

(3) The space afforded by fixed room dividers, such as freestanding bar-type counters or railings

I think the code does say the column would be considered as wall space based on how (1) is written.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I think the code does say the column would be considered as wall space based on how (1) is written.

My interpretation of this (and of course I know I'm right! :evil:) is that it is 24" the maximum distance from a given point. So if it is a 6x6x6x6 column, the furthest would be 6+6 (or 12 for those who don't want to do the math), since once you exceed that you're closer going the other way around. Code says distance to an outlet, it doesn't say how or what path one takes.

However trying to convince an inspector that I'm right will be difficult. :willy_nil
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I think the code does say the column would be considered as wall space based on how (1) is written.
That is why some things are open to interpretation. IMO a simple column is NOT "wall space" or a room divider, or anything similar.

This is also how some inspectors can be on power trips. They think their interpretation is the only valid one. If this were me and an inspector demanded a receptacle on a 6'sq column I'd fight it to the highest level based simply on the absurdity of the demand.
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
My interpretation of this (and of course I know I'm right! :evil:) is that it is 24" the maximum distance from a given point. So if it is a 6x6x6x6 column, the furthest would be 6+6 (or 12 for those who don't want to do the math), since once you exceed that you're closer going the other way around. Code says distance to an outlet, it doesn't say how or what path one takes.

However trying to convince an inspector that I'm right will be difficult. :willy_nil
Unfortunately you definitely are wrong in this. The 24" number is the minimum space requiring a receptacle. Not the minimum distance to a receptacle to a given point. This space is not written the same way the 6' space rule is.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
That is why some things are open to interpretation. IMO a simple column is NOT "wall space" or a room divider, or anything similar.

This is also how some inspectors can be on power trips. They think their interpretation is the only valid one. If this were me and an inspector demanded a receptacle on a 6'sq column I'd fight it to the highest level based simply on the absurdity of the demand.

:thumbup::thumbup::thumbup::thumbup:
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Do you have enough room to put an outlet on the column? If so, put one there. In the future you'll probably be surprised that you use it often!
I agree, if there is room to put in the outlet, then do it. I am a firm believer in principles and "what's right is right", but the thing is, some fights are just not worth fighting. Besides, as you suggested, he will probably end up using the outlet a lot more than he thinks he will anyway.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I agree, if there is room to put in the outlet, then do it. I am a firm believer in principles and "what's right is right", but the thing is, some fights are just not worth fighting. Besides, as you suggested, he will probably end up using the outlet a lot more than he thinks he will anyway.
Thing is, if the column is 6x6 and is hiding a 4" lally column, how much room do think actually exists to install a receptacle box?? Nearly none is the answer.

Now he'd have to modify the whole column to be at least 6x8 just to accommodate the receptacle. Some fights ARE worth fighting.
 
OP
A

Al G

Well-known member
Joined
Jan 5, 2015
Messages
340
Location
Arizona
As some have said, I don't want to make the column larger just to fit a receptacle. Given where the column is we want to keep it as small as possible. There is no way I would ever use an outlet in that location.

My plan is to box it in with 1x after ceiling and floor are finished. If I keep the boards tight to the steel column I'll end up with 5.5" sides. I just hope he doesn't measure at baseboard level. Who knows what might happen to that column after the inspection.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Unfortunately you definitely are wrong in this. The 24" number is the minimum space requiring a receptacle. Not the minimum distance to a receptacle to a given point. This space is not written the same way the 6' space rule is.

but I gave it a good try! :lol:
 