Can I run a load "backwards" through the feed from main panel

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
I have a 400A main panel on a pedestal feeding two 200A subpanels, one on the shop and one on the house. Due to a perfect storm of weird coincidences I would like to do something odd. I can't find the right google terms to find an answer. The house panel is pretty full with water heaters, two ACs, hot tub - living the American dream. Wife wants to add huge pottery kiln on the house side.

Over in the shop I have the typical big loads that never run all at once; lift, compressor, welder, plasma, mill, lathe. Also, as a result of another screw-up, the feed from the 400A panel to the shop is a 20 foot run of - no lie - 3 inch EMT (don't ask).

So, I'd like to add a 60A breaker to the shop subpanel to feed a new kiln in the house. It would really simplify my work if a could shove the wire from that breaker back through the feed from the 400A (plenty room in 3 inch EMT) and loop it through the main panel and run it out to kiln. In my mind of course it will work, but is there something not code kosher about running a load back through the shop subpanel feed?
 
To avoid these ads, REGISTER NOW!

patrickoneal

Well-known member
Joined
Mar 9, 2009
Messages
75
I have a 400A main panel on a pedestal feeding two 200A subpanels, one on the shop and one on the house. Due to a perfect storm of weird coincidences I would like to do something odd. I can't find the right google terms to find an answer. The house panel is pretty full with water heaters, two ACs, hot tub - living the American dream. Wife wants to add huge pottery kiln on the house side.

Over in the shop I have the typical big loads that never run all at once; lift, compressor, welder, plasma, mill, lathe. Also, as a result of another screw-up, the feed from the 400A panel to the shop is a 20 foot run of - no lie - 3 inch EMT (don't ask).

So, I'd like to add a 60A breaker to the shop subpanel to feed a new kiln in the house. It would really simplify my work if a could shove the wire from that breaker back through the feed from the 400A (plenty room in 3 inch EMT) and loop it through the main panel and run it out to kiln. In my mind of course it will work, but is there something not code kosher about running a load back through the shop subpanel feed?


Why not just feed another subpanel or disconnect off the 400A main panel for the kiln? That seems like the simplest thing to do, but I haven't seen what you've got.
 

buddyboy

Well-known member
Joined
Oct 8, 2007
Messages
616
I'm not an electrician.

Can he change the service to the house to a 400 amp service, then from that 100 amp subpanel out to the shop. this way he will have more than enough at the house to run whatever?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
I have a 400A main panel on a pedestal feeding two 200A subpanels, one on the shop and one on the house. Due to a perfect storm of weird coincidences I would like to do something odd. I can't find the right google terms to find an answer. The house panel is pretty full with water heaters, two ACs, hot tub - living the American dream. Wife wants to add huge pottery kiln on the house side.

Over in the shop I have the typical big loads that never run all at once; lift, compressor, welder, plasma, mill, lathe. Also, as a result of another screw-up, the feed from the 400A panel to the shop is a 20 foot run of - no lie - 3 inch EMT (don't ask).

So, I'd like to add a 60A breaker to the shop subpanel to feed a new kiln in the house. It would really simplify my work if a could shove the wire from that breaker back through the feed from the 400A (plenty room in 3 inch EMT) and loop it through the main panel and run it out to kiln. In my mind of course it will work, but is there something not code kosher about running a load back through the shop subpanel feed?

No u cant do that. As has already been said, u cant have 2 feeds to a structure. BTW does this EMT run underground?

Why not do a subpanel off the panel in the house? Move one circuit(240v) from the house panel to the subpanel to free up a breaker space...

I'm not an electrician.

Can he change the service to the house to a 400 amp service, then from that 100 amp subpanel out to the shop. this way he will have more than enough at the house to run whatever?

U mustve not read the OP. He said he HAS 400a service. Moving that to the house from the pedestal would be cost probibitive. he already has 200a in the shop so why would he change that to 100a? :headscrat

The real issue is space in the house panel....so do a subpanel off the house subpanel.
 
Last edited:
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
Actually it 3 inch EMT up the wall, then turns into 3 inch schedule 80 CPVC to complete the run underground.

The other thing that sticks in my mind is the 10kW solar system is on the shop backfeeding that subpanel so I favor using that subpanel for additional loads. But after thinking about this post I'm starting to feel stupid. The solar system doesn't care whether its hooked to the shop subpanel or the 400A panel.

I think I can terminal block into the 400A panel for the kiln, that solves my problem (still no additional conduit needed). Or subpanel the house subpoena. That's a good idea too.
 
Last edited:

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,669
Location
SE MI
So, I'd like to add a 60A breaker to the shop subpanel to feed a new kiln in the house.
IANAE (I am not an electrician), nor a "code lawyer", but somewhere I recall that a building can only have "one feed", so the answer is no.

Now, if the kiln was outside in a shed, the answer would be yes !
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,669
Location
SE MI
Why not do a subpanel off the panel in the house? Move one circuit(240v) from the house panel to the subpanel to free up a breaker space...
Replace a couple of single breakers with tandems. Instant 2 slots.

Unless you have some massive AC units (note plural) I can not imagine that a 200A panel would not have enough capacity.

Tell her to not run the electric dryer for the couple of days the kiln is fired. (Arizona ... who needs a clothes dryer !)
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
No, only one feed to a structure allowed.

In this case I think it would be allowed. The feeder back is not a service and under 2011 NEC 225.30 where a feeder originates in an additional building, one feeder is allowed to provide power back to the original structure.

Edit: Ooops... I'm wrong. I wasn't thinking about the service is at a pedestal feeding two separate 200A panels at separate buildings. I was thinking of the main 400A service being at the house and the shop being fed from the house. I should know better than to question an answer from Norcal.
 
Last edited:
To avoid these ads, REGISTER NOW!

buddyboy

Well-known member
Joined
Oct 8, 2007
Messages
616
yep I got confused, I thought he had 400 amp service at the pedestal with a 200 amp subpanel at the house and a 200 amp subpanel in the shop. with the house actually drawing at almost capacity and the barn not even close to drawing at capacity. I thought the OP was looking to use some of the unused capacity at the shop to power his wifes kiln at the house by running a circuit from the shop to the kiln.

sorry this is why I am not an electrician. My kindergarten teacher was wrong about no stupid questions.

lol
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
yep I got confused, I thought he had 400 amp service at the pedestal with a 200 amp subpanel at the house and a 200 amp subpanel in the shop. with the house actually drawing at almost capacity and the barn not even close to drawing at capacity. I thought the OP was looking to use some of the unused capacity at the shop to power his wifes kiln at the house by running a circuit from the shop to the kiln.

sorry this is why I am not an electrician. My kindergarten teacher was wrong about no stupid questions.

lol
That is correct.

Actually the kiln IS in a "studio" (shed) next to the house....

The 200A at the house is probably not at "capacity" for current, but all the slots are full with important stuff.
 

buddyboy

Well-known member
Joined
Oct 8, 2007
Messages
616
then can't you just put a sub-panel next to your house panel to give you more slots?
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
then can't you just put a sub-panel next to your house panel to give you more slots?
Yes, I was erroneously stuck on the idea that to take advantage of my solar I had to breaker into the shop panel, but after actually thinking about it, both subpanels are paralleled to the pedestal, so it makes no difference.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
U have one meter so thats correct it doesnt matter.

I assume u will have lighting in the shed. I would put a subpanel in the shed. U will need a 4-wire feeder and 2 ground rods. Also, the neutral bus needs to be isolated from the ground bus bar and enclosure...
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
I have two meters, one is for just the solar panels. But, yes, one revenue meter for the main feed from the power company. It runs backwards on a sunny day. I think it is a good idea to just add a subpoena in the shed, I'm going that way.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
51,659
Location
Northern Central Ohio
I have two meters, one is for just the solar panels. But, yes, one revenue meter for the main feed from the power company. It runs backwards on a sunny day. I think it is a good idea to just add a subpoena in the shed, I'm going that way.

IANAE, but I'm guessing autocorrect ?
 