Electrical service on new potential shop

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
Finally decided I need to upgrade from a single car garage to a larger shop, looked at one in my area yesterday, and was curious what you guys think about this electrical? I will be using a 220v welder and 220v 80 gallon air compressor for the largest
equipment..uploadfromtaptalk1430132892236.jpguploadfromtaptalk1430132975586.jpguploadfromtaptalk1430133090055.jpg

Sent from my XT1080 using Tapatalk
 
To avoid these ads, REGISTER NOW!

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Is that something you are buying/renting? looks like someone changed the panel out, but has # 10's feeding it (maybe its temporary?) the service wires do not match the capability of the panel, they are undersized. Looks like # 10's feeding a 200 amp panel.
 
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
I looked at the wires and the say #8 tw , not sure what tw stands for though?

Sent from my XT1080 using Tapatalk
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
They could be #8's. Thats ok to feed a 200a panel as long as the panel capacity isn't exceeded. You need to look at the breaker in the main panel and it needs to be matched to the wire.
Bottom line is you need to bring in a larger wire on an appropriate sized breaker for your wants.
 
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
I looked at the wires and the say #8 tw , not sure what tw stands for though?

Sent from my XT1080 using Tapatalk
To me 8 gauge is not enough to support 200a, and with the 100a and 60a outside is just kind of confusing too me,Also its something I'm thinking about buying, I have one more place to check out, there's really a shortage in decent buildings around here..

Sent from my XT1080 using Tapatalk
 

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
What size breaker feeding it? Weird, setup, what did they do in their before, I seen a building where they had a 200a 40 space panel with all 15 a mini's in it, so A LOT of breakers. Being fed by a 30a breaker with 10 ga wire. It was a "clean" power circuit that ran all the printer and computers at each station in the building. They didn't need a lot of power, just wanted each one on its own breaker so they could shut them down individually, there had to be 30K feet of 14/2 in that building...


Either way it looks like there is a nice big conduit running to it so you can run what ever you want to that panel, depending where it is coming from...
 
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
It was an old gas station years and years ago.. The 60a and 100a is what's feeding the main panel..

Sent from my XT1080 using Tapatalk
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
FWIW the 60 amp breaker is in the tripped position. You have already stated more load than what the wires feeding the panel can carry. Since it appears that this is a sub panel, it needs 4 wires feeding it, and seperate the neutrals and grounds
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
Yeah I noticed that as well, i think I'll have an electrician check it out before I make any decisions..

Sent from my XT1080 using Tapatalk
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
To me 8 gauge is not enough to support 200a, and with the 100a and 60a outside is just kind of confusing too me,l
You are confused by the 200a panel. It is like putting V rated tires on a Yugo.
What is the breaker before the wire? Those are the important ones and should match.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
It was an old gas station years and years ago.. The 60a and 100a is what's feeding the main panel..

Sent from my XT1080 using Tapatalk

If the 60 or the 100 is feeding this panel, the wire is to small. Talk about the issues with the owner, talk about possible wiring violations, his insurance company wouldnt be to happy!! maybe he will fix everything. If you are purchasing the building, see if you can buy it "As Is" and drop the price for repairs :)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,761
8 TW is 40A rated, wire with TW insulation is pretty much unheard of anymore.
 
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
Had an electrician check it out.. Said basically what needs to happen is too add larger wire ... And I forgot the rest of the technical items..bout $500-$1000 he said...

Sent from my XT1080 using Tapatalk
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
You should mark that nuetral white so it doesn't get mixed up in the future. I'm also curious as to why the breaker is tripped
 
OP
K

keith5064

Well-known member
Joined
Mar 16, 2014
Messages
109
There was another little building off to the side and I believe that was supplying power at one time, but that building has been recently torn down..the 100 amp breaker is what goes to the panel I showed....which when I looked at this building I specifically looked at the service..just to make sure things are up to snuff..the owner now knew nothing of this till I brought it too his attention...

Sent from my XT1080 using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
To me 8 gauge is not enough to support 200a, and with the 100a and 60a outside is just kind of confusing too me,Also its something I'm thinking about buying, I have one more place to check out, there's really a shortage in decent buildings around here..

Sent from my XT1080 using Tapatalk

Wow 100a breaker feeding 40a wire...
 