I want to run power from my garage to my 10x16 storage shed.
I only need a few outlets to power battery maintainers. I want an outside motion light for security, and an indoor light to find stuff in the dark.
I'd like to run a multi-wire branch circuit example = one neutral, and two opposing hots on a common trip 20a double pole breaker. one branch for lights the other for outlets.
From the garage sub panel I was planning on 40' of 12/3 NM-B to a junction box then 25' of 12awg THHN wires red black white and green (because I have it already) in 3/4" Flexible Non-Metallic Liquid-Tight conduit buried 12" to 18" deep to the shed then another junction box here I would run 12/2 NM-B to the lights and outlets. All wire properly attached to or run thru studs with proper staples/clamps.
Now the questions..
Can I use a multi-wire branch circuit as my 1 one circuit to the shed so I don't need a sub panel or ground rods.
How does one run the Liquid-Tight conduit from the LB on the house? looking around I haven't seen any PVC ones that are threaded. An explanation of this one would be appreciated. I've done a lot of wiring but not too much to outbuildings
At the shed can I just enter with the Liquid-Tight conduit thru the sil plate under the back corner of the shed? Caulked/clamped in of course.
Can I use the NM-B in the stud cavity's of the shed for my circuits?
Should I use GFCI for the supply breaker($104.00 ouch)? Or is there a cheaper way? maybe one GFCI outlet before the lights and the one gfci first for the outlets.
Anything I'm forgetting? any suggestions? Thanks..
I want to run power from my garage to my 10x16 storage shed.
I only need a few outlets to power battery maintainers. I want an outside motion light for security, and an indoor light to find stuff in the dark.
I'd like to run a multi-wire branch circuit example = one neutral, and two opposing hots on a common trip 20a double pole breaker. one branch for lights the other for outlets.
From the garage sub panel I was planning on 40' of 12/3 NM-B to a junction box then 25' of 12awg THHN wires red black white and green (because I have it already) in 3/4" Flexible Non-Metallic Liquid-Tight conduit buried 12" to 18" deep to the shed then another junction box here I would run 12/2 NM-B to the lights and outlets. All wire properly attached to or run thru studs with proper staples/clamps.
Now the questions..
Can I use a multi-wire branch circuit as my 1 one circuit to the shed so I don't need a sub panel or ground rods.
How does one run the Liquid-Tight conduit from the LB on the house? looking around I haven't seen any PVC ones that are threaded. An explanation of this one would be appreciated. I've done a lot of wiring but not too much to outbuildings
At the shed can I just enter with the Liquid-Tight conduit thru the sil plate under the back corner of the shed? Caulked/clamped in of course.
Can I use the NM-B in the stud cavity's of the shed for my circuits?
Should I use GFCI for the supply breaker($104.00 ouch)? Or is there a cheaper way? maybe one GFCI outlet before the lights and the one gfci first for the outlets.
Anything I'm forgetting? any suggestions? Thanks..

I bought the pull elbow but before I assemble I'll try to get the right one or I'll make the elbow accessible when I close up the walls in the garage.