Circuit breaker for 4 post lift

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
I am installing a 220v line in anticipation of installing my 4 post Bend Pak lift. BendPak says I need a 25 amp circuit breaker. I used 10 2 wire and local code says we need a switch. The only issue is I can find a 20 amp and a 30 amp circuit breaker but not a 25amp. So do I use a 20 or a 30?
 
To avoid these ads, REGISTER NOW!

kabinenroller

Well-known member
Joined
Sep 14, 2013
Messages
905
Location
S.E. Wisconsin USA
Use a 30 amp breaker. Most codes have a percentage of amps that the breaker must exceed the max. Amp draw of the load. I have a 30 for my BendPak, no issues at all.
 

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
wow, I used 12-2 and a 20a breaker for my 2 post forward, the bendpak must pull more amps. Come to think of it I used 12-2 20a for every lift we ever bought...
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
I am installing a 220v line in anticipation of installing my 4 post Bend Pak lift. BendPak says I need a 25 amp circuit breaker. I used 10 2 wire and local code says we need a switch. The only issue is I can find a 20 amp and a 30 amp circuit breaker but not a 25amp. So do I use a 20 or a 30?

Use a 30a. Code allows the use of the next standard size breaker...
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Just out of curiosity, what brand of panel do you have??, 25 amp and 35 amp breakers are starting to be carried by the supply houses, mainly for air condition units, they will have the "Max Fuse or Cir Brkr Size= on the name plate, inspectors are enforcing it closer now.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
A 25 amp breaker is a standard size, which code says you can round up from that when Bendpak specified it?

Looking at NEC 240.6a, I stand corrected. I dont think Ive ever seen or used a 25a breaker but a search at home depot reveals they do have them!

Scratch my previous comment!

Use a 25a!

This is why u dont comment when youre half awake!
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Looking at NEC 240.6a, I stand corrected. I dont think Ive ever seen or used a 25a breaker but a search at home depot reveals they do have them!

Scratch my previous comment!

Use a 25a!

This is why u dont comment when youre half awake!

Supply houses around here carry them, HD and Lowes you usually have to have them shipped to the store

Go get some rest:)
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
Looking at NEC 240.6a, I stand corrected. I dont think Ive ever seen or used a 25a breaker but a search at home depot reveals they do have them!
Scratch my previous comment!
Use a 25a!
This is why u dont comment when youre half awake!


So, if I'm plugging in a 100W light bulb, or my TV that draws 96W, do I have to use a 1A breaker??


And yes, WTF is BendPak using for a motor on their pumps??
25A at 220v is a **** load of power. My "real" 3HP compressor motor only draws 17A at 220V.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I believe all this is made and wrote in China. The Mohawk pretty much refers to the motor, there is a tag on mine, allows 14 wire to 30A
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
My Challenger lift has a 2HP motor and the install manual calls for a 25A breaker. The motor has an additional data label that also shows 20A is the max working load.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It seems I looked at some of the instructions before and found it to recommend something like "certified" electricial and suggest the owner call him. The manual for a welder comes with the data. I suspect there is no loss for Bendpack to use a larger wire since so many think its needed for "220" anyway but the thermal issue could be trump.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
So, if I'm plugging in a 100W light bulb, or my TV that draws 96W, do I have to use a 1A breaker??


And yes, WTF is BendPak using for a motor on their pumps??
25A at 220v is a **** load of power. My "real" 3HP compressor motor only draws 17A at 220V.

Breakers are for protecting inside wiring NOT whats plugged into them...so no u dont use a 1a breaker...

Breakers for motor circuits are only for protection against ground faults and short circuits. Breakers for motor circuits are sized higher than the ampacity of the wire because of in-rush currents that motors have. The overload on the motor or motor starter protects the wiring and motor...So your 3HP motor can have a max breaker size of ~42a....
 
To avoid these ads, REGISTER NOW!

slice

Well-known member
Joined
Jun 16, 2010
Messages
331
Avg four post lift used by avg joe requires no more than 120v 20 amp circuit. It's not heavy or continuous duty !!!! My 2/ 4- post lifts are 120 v 20 amp and work fine.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
I am using a Square D panel and didn't see the 25 amp at HD. Will check online. So here's another question. Since this is an attached garage. Do I use a GFCI circuit breaker? I know for all outside outlets, etc. GFCI is code, but an attached garage is a grey area, neither truly indoors nor outdoors.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Because the 120 is for portable tools, many ungrounded, on general circuits where the user plugs in, some in wet locations. This probably isn't the right thing to say here but I would put a 30 on and forget about it.
This is not something automatic or unattended and I really have some legit doubts who ever wrote the manual knew exactly what they were doing.
USA made outfit would have allowed a 12/30
 
Last edited:

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
435
Location
Mid-Coast Maine---> Eastern Shore Virginia
I have a Bendpak 4 post lift, 120v motor, ran 12/2 wire because Bendpak instructions say to use a 25 amp breaker. The tag on the lift says max draw 20 amps, tag on motor says 17 amps full load current. I have been running it for 3 years with no issues on a 15 amp breaker.
 

JohnnieMo

Well-known member
Joined
Nov 25, 2014
Messages
1,175
Location
Calgary, Alberta
I'm pre-wiring for my lift also. The Lift King rep said I need a 20A 240V breaker. He didn't specify wire. I assume 12/2 is fine.

Get this though... my new Mig Pak 180 welder specified a 40A 240V breaker and 14/2 wire! I had a very hard time believing the wire spec, so I tried it for a job. The wire never even got warm.

When I wire in the plug I'll use 12/2 for it also, but man - 240V really changes the game.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
PattenP

Now you peak my curiosity. Why doe 120v need a GFCI and not 240v?

There is a proposal to require GFCI's on 240V circuits for the next NEC edition, but that is a what may happen, not what is required now.


If a QO225, breaker cannot be found easily, use a QO230, install a 30A fusible switch & install 25A fuses in the switch.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
I'm pre-wiring for my lift also. The Lift King rep said I need a 20A 240V breaker. He didn't specify wire. I assume 12/2 is fine.

Get this though... my new Mig Pak 180 welder specified a 40A 240V breaker and 14/2 wire! I had a very hard time believing the wire spec, so I tried it for a job. The wire never even got warm.

When I wire in the plug I'll use 12/2 for it also, but man - 240V really changes the game.

thats because branch circuits for welders have different sizing than normal branch circuits. Welder circuits are sized based on input current and duty cycle.
 

Sixfeet4

Well-known member
Joined
Jul 27, 2012
Messages
189
Location
Houston, TX
I'm doing pre-wire on my a shop right now and installing a BendPak 2-Post. Also running wire to add 4-post down the road. The local company that sells/installs the lifts told me 220V on 30A breakers for each of the lifts and my air compressor.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
I would use 12-3 (12-4) wire (i.e. three coated wires and bare ground)with a 30amp circuit breaker.
 

JohnnieMo

Well-known member
Joined
Nov 25, 2014
Messages
1,175
Location
Calgary, Alberta
thats because branch circuits for welders have different sizing than normal branch circuits. Welder circuits are sized based on input current and duty cycle.

Interesting. Makes sense. Their duty cycle is quite low. It doesn't cost me much to run a 12/2 anyways. I'll run the same for the lift.

I want to ask why would one add another conductor?