So I go to fire up my welder and nothing. Breaker is in ON position, but I cycle it a few times regardless. Plug in my other welder and still nothing.
Put the DVM across the 2 hot lines at the outlet and I'm only getting 90VAC. Hmmm, it's only about a 6 ft run between the outlet and garage subpanel.
Shut off power to the subpanel, pull the cover, and check connections. All tight. No signs of heat damage or arcing.
Check resistance between both hot lines at the outlet and get infinity. Also get infinity from each hot line to ground or neutral. So no shorts.
Flip the breaker on and check resistance across each line and get zero ohms.
Pull the breaker out of the panel and there is grease, I guess antioxidant, on the terminals.
What next?