A few months ago I installed 5 hard wired surface mount Lowes (F32-T8 lamps x 2) lights on my garage ceiling, using the existing light circuit for their power. I had the lights on, as I was changing a broken 3-way switch cover plate. My left arm was grazing the overhead door metal track that is buried down in the concrete floor, as I was putting the metal screws in to the cover plate with my right hand....
Once when my finger touched the metal blade of my screwdriver, I felt a sharp "tingle" in my left arm that was touching the metal door track. A quick voltage check showed I had a 94 volt reading from my screwdriver blade while it was inserted in to the cover plate screw, to the door track.
I tracked the issue down to an open grounding conductor where the PO had installed a new fixture in the utility room (the garage ceiling lights were fed from it) and he had cut the equipment grounding conductor's off inside the outlet box ... for some reason .
So a trip in to the attic and with some new cable installed, I got the lights grounded and the voltage reading from the 3 -way switch frame to the door track reading "0". Be sure those electronic light ballasts are grounded properly guys !
Once when my finger touched the metal blade of my screwdriver, I felt a sharp "tingle" in my left arm that was touching the metal door track. A quick voltage check showed I had a 94 volt reading from my screwdriver blade while it was inserted in to the cover plate screw, to the door track.

I tracked the issue down to an open grounding conductor where the PO had installed a new fixture in the utility room (the garage ceiling lights were fed from it) and he had cut the equipment grounding conductor's off inside the outlet box ... for some reason .
So a trip in to the attic and with some new cable installed, I got the lights grounded and the voltage reading from the 3 -way switch frame to the door track reading "0". Be sure those electronic light ballasts are grounded properly guys !