Not sure I understand Circuit protection for derated circuits.
I have two 240 volt circuits in a common 3/4 EMT. The EMT caries 4 hot's and 2 neutral's and each branch has several NEMA L15-20 receptacles rated at 20 Amp, 60°.
So technically the wire needs to be derated to 24 AMPS. But my question is does the circuit protection also need to be derated to 24 amps or can I use a 25AMP or 30 AMP breaker.
I see the NEC requires a CB 125% of the continuous load. I would like to plug in a 4800 (20Amps) watt heater. With the 20 amp CB I currently have It would probably blow the breaker and also be in violation of the 125% minimum.
I could also go to a 75° plug but I can only find those in large 50 amp welding receptacle's which I prefer to avoid.