Subpanel - Connecting Ground and Neutral in main panel

Prometheus

Well-known member
Joined
May 17, 2006
Messages
104
So I'm almost done installing my subpanel, and I'm 99% certain how to do the final connections, but I just want a sanity check.

Ground and Neutral have separate bars in the subpanel, neutral is not bonded. In the main panel, neutral IS bonded and all the ground and neutral wires go to the same bar. When connecting my subpanel feeder wires BOTH neutral and ground wires connect to the neutral bus bar, correct? Thanks.
 
To avoid these ads, REGISTER NOW!

jdieter

Well-known member
Joined
Nov 17, 2007
Messages
320
Location
Northern Indiana
Is installing a ground rod for a detached structure sub-panel a NEC requirement? I've been out of the electrical game for several years, the last code book I have is 1996 and I can't find it.
 

Samh

Well-known member
Joined
Aug 16, 2006
Messages
482
Location
Canton GA
Is installing a ground rod for a detached structure sub-panel a NEC requirement? I've been out of the electrical game for several years, the last code book I have is 1996 and I can't find it.

They allow both approaches for a detached structure. but you would only bond at the sub panel if running a ground rod, otherwise ground runs with feeder wires.

For in the same dwelling, you ground back to main panel, which is bonded with neutral.
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
They allow both approaches for a detached structure. but you would only bond at the sub panel if running a ground rod, otherwise ground runs with feeder wires.

For in the same dwelling, you ground back to main panel, which is bonded with neutral.

If I remember correctly right now a detached structure has to have two ground rods if in the US.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
When connecting my subpanel feeder wires BOTH neutral and ground wires connect to the neutral bus bar, correct?

In the main panel? You may have two bus bars, but since they're bonded, each one is the same. Only in the subpanel do you need to worry about keeping neutral and ground on separate bars.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Question...............If you have 4 wires from the main panel, what is the symptom or problem with no ground rod at the remote panel ???

4 wires = 2 power, neutral and ground
 
Last edited:
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
Question...............If you have 4 wires from the main panel, what is the symptom or problem with no ground rod at the remote panel ???

4 wires = 2 power, neutral and ground

I believe the main issue is with lightning and a detached structure.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
You need both a 4 wire feeder and 2 ground rods for a detached structure.
(Unless you PROVE that 1 ground rod would measure less than 25 ohms to ground.)

The ground rod(s) should be connected to the ground bar only.
The neutral must not be bonded to ground.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
OP . . . to get best advice . . . Update GJ Profile with City / State / Country.

Also, GJ Sparkies can give you even BETTER advice if you provide PIC's. Like PIC of your main panel . . . AND . . . PIC of your subpanel. Provide total Amps coming into main panel, and Wire used from main panel to subpanel. Provide length of wire from Main panel to Subpanel. What breaker is in main panel to feed the subpanel ?? What amps do you want / or "need" in garage at subpanel (ie what all electrical loads in garage)??
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Question...............If you have 4 wires from the main panel, what is the symptom or problem with no ground rod at the remote panel ???

4 wires = 2 power, neutral and ground

The purpose of ground rods is to ground lightening, limit the voltage to ground potential, among other things.

People often confused grounding electrodes and EGCs/ground wires.

Heres a good article to read to help u understand the differences:

http://www.electriciantalk.com/articles/the-confusion-of-the-term-grounding/

Location is a factor in ontario canada you only ground a service at the point of entry

Ive never understood Canada's logic with that...
 
OP
P

Prometheus

Well-known member
Joined
May 17, 2006
Messages
104
Thanks for the replies.

Is this subpanel in a detached structure? If so, you will need ground rods at the subpanel location.

Attached garage, sorry, forgot to mention that in my original post.


Not that it really matters, but I live in Michigan. It's a 55 foot run of AL SER 2-2-2-4 going from a 125 amp main panel with a 50 amp breaker to the subpanel with just main lugs in the garage. Yes, I could breaker it at a 70 amp, but I already have the 50 amp breaker from an old (removed) circuit and I don't think I will be running anything big enough to draw more than 50 amps. Also, main panel only has one bus bar.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Thanks for the replies.



Attached garage, sorry, forgot to mention that in my original post.


Not that it really matters, but I live in Michigan. It's a 55 foot run of AL SER 2-2-2-4 going from a 125 amp main panel with a 50 amp breaker to the subpanel with just main lugs in the garage. Yes, I could breaker it at a 70 amp, but I already have the 50 amp breaker from an old (removed) circuit and I don't think I will be running anything big enough to draw more than 50 amps. Also, main panel only has one bus bar.

First off #2 AL SER is good for 90a if not buried in insulation.

I assume youre referring to the neutral bus bar.
 
OP
P

Prometheus

Well-known member
Joined
May 17, 2006
Messages
104
First off #2 AL SER is good for 90a if not buried in insulation.

I assume youre referring to the neutral bus bar.

Correct, one neutral bus bar.

And you're right, 90 amp is my max. For some reason I was stuck on the 65* column in the ampacity table instead of the 75* column. I figured if I'm doing this, I'm only pulling cable once. At least this way if I want to upgrade later all I have to do is swap the breaker.
 