Easy to turn this into an outlet?

MagicMarker

Well-known member
Joined
Aug 20, 2014
Messages
578
Location
NJ
This is the lone 3 way switched light fixture (just a lone porcelain bulb holder) in the garage. I'd like to turn it into an outlet so I can plug in an LED shop light. I'd also like to add 3 or 4 more outlets through out the ceiling to add more LED lights. In my head, this is a fairly straight forward project. Please let me know if I'm over simplifying it.

1C82BFC4-E274-4BFA-812E-3B24A2F8F35A_zpshhicyz4g.jpg
 
To avoid these ads, REGISTER NOW!

94EG8

Well-known member
Joined
Apr 5, 2015
Messages
248
You can do this in one of two ways.

If your code permits it you can use an outlet cover for an octagon box like so:

4-Flat-Duplex-Outlet-Octagon-Junction-Box-Cover-SCV-20270-.jpg


or you can replace the octagon box with a regular receptacle/switch box.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,325
Location
Alexandria, VA
Just a guess but, there is probably constant 120 volts running to the ceiling box, and the other cable runs to the wall switch where you turn it on and off for the light. If that is the case you can connect an additional 120 volt line out of the box (it appears to be large enough capacity) and use that to power additional lights or receptacles. Depending on how you wire it, the receptacles could be switched on by the existing switch, or they could be always live.

Bruce
 
OP
M

MagicMarker

Well-known member
Joined
Aug 20, 2014
Messages
578
Location
NJ
You can do this in one of two ways.

If your code permits it you can use an outlet cover for an octagon box like so:

4-Flat-Duplex-Outlet-Octagon-Junction-Box-Cover-SCV-20270-.jpg


or you can replace the octagon box with a regular receptacle/switch box.

Didn't know that those existed. I could do that or for consistency sake, I'd like to change it to a regular box.

31yIQPVbqlL._SX300_.jpg



just screw it in....

Just bought one of those... will use that temporarily until I get more lights.

Just a guess but, there is probably constant 120 volts running to the ceiling box, and the other cable runs to the wall switch where you turn it on and off for the light. If that is the case you can connect an additional 120 volt line out of the box (it appears to be large enough capacity) and use that to power additional lights or receptacles. Depending on how you wire it, the receptacles could be switched on by the existing switch, or they could be always live.

Bruce

That one light fixture box is controlled by two switches.. one in the house and one in the garage. I'd like to run a few more outlets that will turn on/off with those switches.. I'll have to go up there and take a photo of what's in the box and hopefully you can give me guidance.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Any 120 Volt receptacle in a garage (even on the ceiling) requires GFI protection.

The receptacle option with the octagon cover isn't designed for a GFI outlet and would require a GFI breaker

GFIs need to be readily accessible, and a ceiling mounted GFI that needs a ladder to get to isn't.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Any 120 Volt receptacle in a garage (even on the ceiling) requires GFI protection.

The receptacle option with the octagon cover isn't designed for a GFI outlet and would require a GFI breaker

GFIs need to be readily accessible, and a ceiling mounted GFI that needs a ladder to get to isn't.

Thinking the same thing....
 
OP
M

MagicMarker

Well-known member
Joined
Aug 20, 2014
Messages
578
Location
NJ
Any 120 Volt receptacle in a garage (even on the ceiling) requires GFI protection.

The receptacle option with the octagon cover isn't designed for a GFI outlet and would require a GFI breaker

GFIs need to be readily accessible, and a ceiling mounted GFI that needs a ladder to get to isn't.

Is there an easy way for me to do that?
 
To avoid these ads, REGISTER NOW!

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,077
Location
Seacoast New Hampshire
Easiest solution is to use one of those screw-in adapters if you're just going to plug in some lights.

That looks like old ungrounded armored cable (BX). If you're going to add an outlet it either must be a two-pronged outlet or a GFCI. The armor cladding cannot be used as a ground.
 
OP
M

MagicMarker

Well-known member
Joined
Aug 20, 2014
Messages
578
Location
NJ
Any 120 Volt receptacle in a garage (even on the ceiling) requires GFI protection.

The receptacle option with the octagon cover isn't designed for a GFI outlet and would require a GFI breaker

GFIs need to be readily accessible, and a ceiling mounted GFI that needs a ladder to get to isn't.

Easiest solution is to use one of those screw-in adapters if you're just going to plug in some lights.

That looks like old ungrounded armored cable (BX). If you're going to add an outlet it either must be a two-pronged outlet or a GFCI. The armor cladding cannot be used as a ground.

If I run additional outlets off that box, can the boxes be plastic?
 

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,077
Location
Seacoast New Hampshire
Code-wise I'm not sure you can extend a circuit which does not have a ground, but I'm not an electrician. It has nothing to do with plastic vs. metal boxes or romex vs. BX armored cable. I think at the very least you would need to install a GFCI at that junction box and feed additional outlets from the load side of the GFCI.
 