UF cable in water pipe? Meet code? How many conduits in a trench?

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
We are getting solar put on our barn & I'm doing the trenching (solar guys are going to be dropping in their own conduit). While I'm at it, I'm going to be trenching out to the chicken coop as well.

Solar guys are going to be pulling permits & getting inspections for their stuff, so I don't want to cause any problems for them when the inspector shows up. Colorado sticks with NEC, but I can't find clarification on direct bury stuff in unrated conduit. I want to do it safe & right as well as meeting code.

Is it kosher to put one or 2 runs of UF (direct bury) rated cable inside of water pipe? I'm assuming this belt & suspenders approach would be fine & future proof, but not sure. I know water pipe isn't considered kosher as conduit, you need PVC for that, but I'll be using direct bury rated cable buried at least 2' down. I'm planning on actually running 3 1" black poly water pipes. First 4' down for water, one for power & the 3rd for some direct bury rated Ethernet (sprinkler control & a coop monitor) 2-3' down. I was planning on sleeveing things with metal or schedule 80 from the bottom of the trench where to the box (which I believe is required by code).

I'm also looking at the same question for running 100@ service out to the shop/barn. We are quite likely going to end up cutting my existing 50@ service trenching out to the barn. I'm figuring it might be easier to not worry about avoiding it & just use it as a good excuse to upgrade to 100@ capable wire. I don't want to try to use the solar conduit, so will run my own in the same trench. What is code relating to how many high & low voltage conduits you can drop in a trench?
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,218
Location
SE MI
Is it kosher to put one or 2 runs of UF (direct bury) rated cable inside of water pipe?
.
.
.
I'm also looking at the same question for running 100@ service out to the shop/barn.
Are these 2 different circuits, because you are not going to find UF big enough to carry 100A!

I would be surprised if any inspector allowed use on non-electrical rated conduit.

You need the experts here to discuss your 100A service. If you can keep it down to 90A (at the panel you are tapping into) you can likely use MHF aluminum wire. This is direct bury rated and is very cost effective. The size depends on the distance,
 
OP
F

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
I'm not as certain on the 100@ stuff yet. I haven't seen any UF bigger than 10, maybe 8 gauge, although there is other direct bury rated stuff that is good for the amperage I'm looking for. The 100@ cable is likely to end up in PVC to make my life easier trying to comply with codes. I haven't finished crunching the numbers & trade-offs to see if it would be worth it to run direct bury 100@ cable in 1.5" water pipe vs. appropriate cable in 1.5" PVC.

My main concern is being able to use water pipe for a pair of 15-20@ circuits & some low voltage stuff to make my life & future stuff easier & still not get an inspector concerned.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,140
Location
Minneapolis
Is there a reason you want to use water pipe instead of electrical conduit? It's not going to be approved for electrical use no matter what.
 
OP
F

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
Cost & ease of install. It's a lot easier to get a 100' (or 300') of black plastic pipe & put it in a non-straight trench than glue up sticks of PVC. I keep hearing there is poly pipe rated to be used as electrical conduit, but haven't been able to find any sources locally. The one or 2 I tracked down on the Internet was 3-4 times the cost of PVC sticks.
 

thewatusi

Well-known member
Joined
Dec 27, 2013
Messages
1,256
Location
Philly Burbs
How long does it take to glue 10 (or 30) sticks of pvc together? 15 minutes once they're all layed out? 20 at the most?

Just do it right.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
Rockwithjason's right.

Waterpipe doesn't fit the requirements

2011 NEC

353.1 Scope. This article covers the use, installation, and construction specifications for high density polyethylene (HDPE) conduit and associated fittings.

353.6 Listing Requirements. HDPE conduit and associated fittings shall be listed.
______________________________________________________________

You'd be a lot better of going with PVC from end to end, and using THWN rather than UF in all of these applications. (For instance only one 12/2 UF cable can be run through a 3/4" conduit, vs. 15 individual THWNs being to Code in the same conduit)
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Do it right and be done with it already!

Sheesh!

^ ^ ^ This !! OP listen to GJ Sparkies who are telling you straight up !! ;)

Use 2" sch 40 plastic conduit (electrical) for the buried portion and sch 80 once above ground. If your distance isn't too far, the MHF Al 2-2-2-4 is cost effective at approx $1.50/ft for the wire which will give you 90A.

Use you continuous plastic water pipe for your low-voltage stuff (internet, CATV, phone, security, etc). Thus, dig deep trench and put 2" conduit for electric at bottom in some sand. Backfill 12" dirt, then put in your low voltage conduit. Backfill some more, then put in caution tape . . . just for future safety proofing !! :bounce:
 

KiltLifter

Well-known member
Joined
Aug 31, 2012
Messages
106
Location
Lafayette, CO
You might also find it easier to use the straight sticks than wrestle with the coil of pipe.

Also, even for your low voltage - the water pipe may collapse after back-fill (because there'll be no water pressure!) and you might never be able to upgrade to cat7 or fiber or RG600 (in case your peeps want cable and UHDTV!).
 
To avoid these ads, REGISTER NOW!
OP
F

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
Thanks for the reality check. Sounds like water pipe will be fine for the low voltage, but I'll need to still do PVC for even the low amperage 120v.

I really want to use conduit rather than direct bury for all the stuff I'm forgetting. If I need more power or to upgrade something, I just use the pull string rather than digging another trench.

I was thinking I could future proof things with water pipe conduit & get away with it not being rated by using direct bury. Sounds like consensus is that's not a great idea.

Sent from my A0001 using Tapatalk
 

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
If you are just using it as a sleeve for the UF cable then the pipe is fine.

It's pretty common to plow in poly roll pipe to run UF through later.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
water pipe is fine until.... years later someone digs into it thinking its the water pipe they are looking for to tee off of and cuts it with a saw expecting to get wet and gets ssshock instead.:shocking:
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
water pipe is fine until.... years later someone digs into it thinking its the water pipe they are looking for to tee off of and cuts it with a saw expecting to get wet and gets ssshock instead.:shocking:

I use PE water pipe for sewer force mains too and have always wondered if some idiot will try and use it for domestic water. Same pipe. Same size. Same color.

I have worked with lots of 300 foot rolls of PE water pipe. It is not much fun. I would much rather glue together full length sticks of electrical conduit. It's a one step glue not primer and then glue, the sticks come with a **** connector formed onto each end. It is flexible enough to handle a not perfect trench. And of course it is the proper material.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
This thread reminded me of this: :bounce:

I had an electrician from Mexico as an apprentice once, and he told me how in-slab conduits are done down South.
They grease up a garden hose and lay it in the slab before pouring the concrete. (Very little cement mixed way way too much sand and aggregate the size of golf balls)
When the slab dries, they'll pull the greased hose out so they can use it again on the next job.

Voila= Instant pre lubed conduit! :wtf:
 
OP
F

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
Finished the trenching today, 2' deep for power, 4' where the water will be buried. I have a pile of grey 3/4" PVC electrical conduit & 90 degree sweep corners sitting next next to the trench read to glue up. Poly pipe & frost free hydrants should be here tomorow.

I'll be puling in THWN-2 or something else appropriately rated. I'm planning on pulling 10 gauge 2 pair & 3 pair. Does anybody sell this bundled? Home Depot only has single spools, either to short or way to long. And you dont want to pull the wires one at a time, a lot easire to pull all of them through at the same time.

Any suggestions for procuring wire in an easy to pull format without getting 6 huge spools & ending up with a lot of leftovers?

Sent from my K00C using Tapatalk
 
OP
F

Fallon

Well-known member
Joined
Jul 18, 2013
Messages
113
Location
Parker, CO
2 100-250 watt automatic waterer heaters, a couple light bulbs, maybe a dozen watts of Raspberry Pi automation stuff, 50 watts of occasional linear actuators & probably another 100-500 of heaters of various sorts during the winter. So ya, WAY under 30@.

I'm running 10ga to fight voltage drop. Although resistive heaters, light bulbs & wall wart transformers really won't care to much about voltage drop.

And, ya, spent some quality time on that very webpage a month or 2 ago. According to it I can stuff up to 10 10ga wires in the 3/4" conduit & have mostly installed already. Worst case scenario I'm planning on 2 circuits, 1 with a 3 way switch, so 7 wires. Could stuff 16 in if I drop to 12ga & still be fine for amp ratings.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
2 100-250 watt automatic waterer heaters, a couple light bulbs, maybe a dozen watts of Raspberry Pi automation stuff, 50 watts of occasional linear actuators & probably another 100-500 of heaters of various sorts during the winter. So ya, WAY under 30@.

I'm running 10ga to fight voltage drop. Although resistive heaters, light bulbs & wall wart transformers really won't care to much about voltage drop.

And, ya, spent some quality time on that very webpage a month or 2 ago. According to it I can stuff up to 10 10ga wires in the 3/4" conduit & have mostly installed already. Worst case scenario I'm planning on 2 circuits, 1 with a 3 way switch, so 7 wires. Could stuff 16 in if I drop to 12ga & still be fine for amp ratings.

As sherry said - one circuit.

I would do a 10ga MWBC fed to a small panel. That would give you 2x30A, or 2x20A if voltage drop necessitates it.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Breaker at 20 and don't need secondary ocpd,,, ha MWBC is good for V drop on circuits with heavier loads.
 