pex manifold locations

gogolf0401

Well-known member
Joined
Mar 25, 2015
Messages
154
Location
West central MN
Hi Guys,
So I have a 40x88' pole barn that I will be adding radiant heat to. I would like to have 3 zones. 1 zone for a game room and bathroom, 1 zone for wood shop, and 1 zone for the rest which will be storage and mechanics shop.

I'm looking for ideas on where to locate the manifold(s) and what the pump setup should be.

Blue Ridge Company sold me 3 manifolds, 1 for each zone. I've always seen manifolds pretty close together along with the boiler and pump right there. I am unsure how to do it with multiple zones though. I still assume the manifolds need to be close to each other, but how do you do that if you can only use the outside walls (interior walls won't be up till after concrete) to mount the manifolds prior to pour?

Blue Ridge also said I would need 3 pumps, 1 for each zone. I always thought I could just use 1 pump, 1 boiler and use shutoff valves to control which zones get heat.

If any of you have had a similar situation I would be grateful to hear what you guys did. See my floorplan attached.

Thanks!
 

Attachments

  • shop 2.JPG
    shop 2.JPG
    42.8 KB · Views: 37
To avoid these ads, REGISTER NOW!

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
Only one zone here but you might consider locating the close to your utilities...Walter supply, electric, N. gas, etc.
 
OP
G

gogolf0401

Well-known member
Joined
Mar 25, 2015
Messages
154
Location
West central MN
Has anyone brought their pex up out of the concrete to where they were planning to have an interior wall put up? If so, how did you suspend the pex during the concrete pour? Did you hang your manifold from the ceiling or something so you could pressure test before and during the pour?

Given my layout, it would seem best if my mechanicals were installed on the interior walls, that way the 3 manifolds (1 for each zone) can be located relatively close together.

Thoughts?
 

50cal

Well-known member
Joined
Sep 20, 2009
Messages
100
Use a couple 2x4s and a sheet of plywood to suspend from the floor joists.
 
To avoid these ads, REGISTER NOW!
OP
G

gogolf0401

Well-known member
Joined
Mar 25, 2015
Messages
154
Location
West central MN
See photo

This pic appears to show a setup against an outside wall. I need to know how people do it on an interior wall location that is not there yet until after the concrete is poured/cured.

Is this simply not an option? Has no one ever done this?
 

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
I've seen it done, there is a strip of concrete left out, say 12" x 48" the tubing is held up by a couple of posts. Then after the rest is poured the forms are torn out and that area gets poured.
 

jlckmj

Well-known member
Joined
Dec 7, 2009
Messages
732
Location
SE Wiscosin
I used a 2x6 and drilled the holes for the pex, then pushed it down close to where the finished concrete would be and drove 1 1/2 inch angle into the ground to hold it in position. 2x6 is still there, they hand troweled under it to finish.

Jim
 

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I placed 2 vertical pieces of rebar and tied 2 horizontal pieces between them. 1 right a the slab and the other about 24' up. Tied the pex to each horizontal piece paired up so I could easily identify the loops.
 