I just finished running power from my house to my small cabin. 30 AMP feed from house to a SQUARE D 100 AMP box in cabin. 8 gauge wire. Question. I have a box bonding screw left over. Do I need to use it? I do have a ground rod outside with a ground wire run into box. Thanks, Jim
1)The answer is
NO, you will not use it in your application.
2)Then, as Wileys stated: You need to install another bus bar in your panel just like the one your neutrals (whites) and grounds (bare copper wires) are connected to now. They make kits for this.
You will then move your ground wires (the bare copper ones) off of that bar and onto the new bar.
Ok, so why? The green screw you have is used to electrically connect the current metal bus bar holding the grounds and neutrals to the metal in the box. Since you will be using the current bar for the neutrals only, and since your application requires separation of the grounds (bare copper wires) and the neutrals (the white ones), you can throw the screw away. Your grounding bar kit that you will moving the ground wires to, will need to be electrically connected the metal in the panel. This will (should) be accomplished with the screws it comes with.