Ground screw question

Youngfd

Well-known member
Joined
Dec 9, 2014
Messages
189
Location
Maltby, WA
I just finished running power from my house to my small cabin. 30 AMP feed from house to a SQUARE D 100 AMP box in cabin. 8 gauge wire. Question. I have a box bonding screw left over. Do I need to use it? I do have a ground rod outside with a ground wire run into box. Thanks, Jim
 

Attachments

  • IMG_8658.JPG
    IMG_8658.JPG
    135.5 KB · Views: 147
  • IMG_8659.JPG
    IMG_8659.JPG
    116.2 KB · Views: 67
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
Did u run a 3-wire or 4-wire feed?

Looks like 4-wire which is required.

If 4-wire, then u dont need the bonding screw and u will need to get a sq d ground bar kit and move any EGCs/grounds over to the new bar.

What size wire did u run?
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
I just finished running power from my house to my small cabin. 30 AMP feed from house to a SQUARE D 100 AMP box in cabin. 8 gauge wire. Question. I have a box bonding screw left over. Do I need to use it? I do have a ground rod outside with a ground wire run into box. Thanks, Jim

1)The answer is NO, you will not use it in your application.

2)Then, as Wileys stated: You need to install another bus bar in your panel just like the one your neutrals (whites) and grounds (bare copper wires) are connected to now. They make kits for this.

You will then move your ground wires (the bare copper ones) off of that bar and onto the new bar.




Ok, so why? The green screw you have is used to electrically connect the current metal bus bar holding the grounds and neutrals to the metal in the box. Since you will be using the current bar for the neutrals only, and since your application requires separation of the grounds (bare copper wires) and the neutrals (the white ones), you can throw the screw away. Your grounding bar kit that you will moving the ground wires to, will need to be electrically connected the metal in the panel. This will (should) be accomplished with the screws it comes with.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
To further explain, u dont want a bonded neutral bar in a subpanel because u could have neutral return current flowing on grounded metal pathways which would create a shock potential.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,630
Location
SE MI
Aren't you supposed to have (2) ground rods, too? We put them in when I upgraded my service.

In theory you can use 1 but only if the inspector has the proper testing equipment to approve it. 2 is the guaranteed-to-pass way to go.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
Aren't you supposed to have (2) ground rods, too? We put them in when I upgraded my service.

Tommy

In theory you can use 1 but only if the inspector has the proper testing equipment to approve it. 2 is the guaranteed-to-pass way to go.

Inspectors dont test ground rod impedance.

It is upto the installer to PROVE to the inspector that there is 25ohms or less impedance with one rod. Otherwise, 2 are required!
 
OP
Y

Youngfd

Well-known member
Joined
Dec 9, 2014
Messages
189
Location
Maltby, WA
Thanks for all the help. Picked up the ground bar kit and pulled all the grounds off of the neutral bar.
 

Attachments

  • IMG_8668.JPG
    IMG_8668.JPG
    100.7 KB · Views: 52

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
You could have just twisted one around a screw and connected them all with a wire nut - ground bar method is much better.

Do you have a local disconnect that isn't shown in the cabin?
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
You could have just twisted one around a screw and connected them all with a wire nut - ground bar method is much better.

Do you have a local disconnect that isn't shown in the cabin?

He's got less than 6 in the panel.
 
Last edited:
To avoid these ads, REGISTER NOW!