Rnbuck01
I replaced the defrost timer circuit board on our Heil heat pump, and now it's acting like it's not kicking in at all. Is there a reset button for it? I replaced the board because it wasn't going into defrost.
bazar01
Leesburg, GA
Once the thermostat is calling for heat stage 1, the compressor/fan contactor and reversing valve should be energized with 24V. Check that first. I am not sure if Heil reversing valve is energized in heating mode though so check that too.
The defrost control board should start to work once the unit is already operational and the outdoor coil is blocked with frost.
usa#1
The Heil(s) I've seen energize reversing valve for A/C. Check the defrost thermostat to make sure it's working correctly.
R
Rnbuck01
I replaced the board and got heat pump working. Where do I check the defrost thermostat at, or is it just jumpering the two terminals on the board?
bazar01
Leesburg, GA
It still won't defrost.
Is the condenser coil surface blocked with frost and it still won't defrost?
The defrost sensor could be bad or not making good contact with the refrigerant line if you install a new control board. If there is no defrost sensor, the defrost cycle is time based.
See if the board has test pins for forcing the defrost cycle. If there are test pins, try shorting the pins and see if the unit goes to defrost mode. You should hear the reversing valve change state and start melting the frost build up. Then troubleshoot from tere on.
R
Rnbuck01
Yes, the condenser is covered with frost. Which pin on the circuit board does the sensor get plugged into? Does the reversing valve get 24 volts once it goes into defrost? If I jump the board and I should be getting power to the reversing valve, and if there's power there going to the reversing valve, possibly a bad reversing valve?
bazar01
Leesburg, GA
1. Which pin on the circuit board does the sensor get plugged into? Not familiar with Heil. Does the board has a terminal that is labeled "DFS"? Check the electrical schematics on the back of the condenser electrical section cover.
2. Does the reversing valve get 24 volts once it goes into defrost? Depends of how the thermostat is programmed. It can be energized (24VAC) in cooling or heating. If you have an old thermostat, reversing valve terminal is "O" if energized in cooling and "B" if energized in heating.
3. If I jump the board and I should be getting power to the reversing valve,and if there's power there going to the reversing valve, possibly a bad reversing valve? If you jump the test pins, it should go to defrost mode and hear a swoosh which indicates the reversing valve changed state.Does the board have test pins?
RivennHewn
PNW
This is what I had to deal with today, and by 'deal with' I mean I actually had to make a call to the install company and ask for a tech to come fix it.:lol:
RivennHewn
PNW
Didn't get a chance to talk to the tech much, just said it was an easy fix.
R
Rnbuck01
Seems like it will go into defrost manually by jumping the pins, but won't do it manually.
R
Rnbuck01
I went out to test the defrost thermostat sensor and got an OL on my meter which means it's open. If that sensors bad, will it cause it to not go into defrost?
bonneyman
Desert SW
Defrost sensors or thermostats are normally open, closing when the coil temp drops to a certain point (typically around 28 deg F). Disconnect the sensor if you can, and drop it in a glass of icy salt water. It should close (i.e. have continuity) within about 3 minutes.
Usually I recommend replacing the defrost sensor when I do a board, just to prevent this kind of situation.
bonneyman
Desert SW
I got a sensor coming. So will it go into defrost if it's above 28 degrees?
The sensor is measuring coil temperature, not outside air temperature. And usually it's located near the end of the evap coil circuit - the last place to get cold.
So, if it's measuring 28 deg at the end of the coil, the board assumes the coil is sufficiently blocked to need defrosting.
bazar01
Leesburg, GA
If the sensor is normally open, why don't you just put a jumper across the sensor wires? It will simulate the closed contacts and will force a defrost cycle. Then you will know if the sensor is bad unless the sensor is a variable resistor.