6-30 receptacle to welder

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
the 6-30 seems like the receptacle to use for 30 amp 220v garage appliances, like compressor or garage heater, because the other styles have a neutral involved and meant for a dryer.

Anyway, welders I have seen to come with 6-50 plug even though they calls for a 30 amp breaker. So to use such a welder is it advisable to get a 6-30 plug and a 6-50 welder receptacle, 6 gauge wire to make an adapter? (only plugged in when in use, and assuming a dedicated 50 amp circuit is not available, nor is needed for what the welder calls for).

The 6-30 and 6-50 difference is about 1 prong being horizontal and most of the plugs can be configured for either by adjusting the prong orientation.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The welder is designed to be plugged in to 50a circuits provided the wire is 12 or better. The manuals are really written for electric professionals. If the minimum wire which is 14 then the maximum breaker is 30
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
An adapter for these could use 12 wire on circuits to 50.. If it is used on 30 it could be 14 but for the fact that the recept isnt listed for use with that small conductors. The only machines that need better than a 12 in pipe or 10 cable are 250 amp wire feeds which may have a high duty cycle.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
the 6-30 seems like the receptacle to use for 30 amp 220v garage appliances, like compressor or garage heater, because the other styles have a neutral involved and meant for a dryer.

Anyway, welders I have seen to come with 6-50 plug even though they calls for a 30 amp breaker. So to use such a welder is it advisable to get a 6-30 plug and a 6-50 welder receptacle, 6 gauge wire to make an adapter? (only plugged in when in use, and assuming a dedicated 50 amp circuit is not available, nor is needed for what the welder calls for).

The 6-30 and 6-50 difference is about 1 prong being horizontal and most of the plugs can be configured for either by adjusting the prong orientation.

For motor driven equipment, the choice of outlet and plug really depends on the motor horsepower rating. If over 3 hp the equipment will need to be hardwired as standard NEMA plugs and outlets are not rated for more than about 3 hp.

Circuits for Welders have different wiring circumstances than general use circuits.

With that being said, what model welder do u have or will be getting?
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
For motor driven equipment, the choice of outlet and plug really depends on the motor horsepower rating. If over 3 hp the equipment will need to be hardwired as standard NEMA plugs and outlets are not rated for more than about 3 hp.

Circuits for Welders have different wiring circumstances than general use circuits.

With that being said, what model welder do u have or will be getting?

hp is 5 as the product title says for the compressor, but running amp is 22 amp. The motor is not continuously running but I guess when sand blasting it does.

I would really like to use a plug setup if possible and not breaking code

The welder I want is AHP alphatig 200x
 

Daedalus

Well-known member
Joined
Sep 28, 2009
Messages
6,017
Went though this recently. Had 6-50 outlets, which are fine for the Miller 211. Then bought the Lotos plasma cutter, which has a L6-30 plug.

Adapters are common in the electric vehicle world. I tried buying one from an online source, but they were out of stock.
http://evseupgrade.com/?main_page=product_info&products_id=18

So I just bought a 2' cable from lowes and the plugs from Amazon to make my own.
http://www.amazon.com/gp/product/B000VL6X22/?tag=atomicindus08-20
http://www.amazon.com/gp/product/B0095GKC8U/?tag=atomicindus08-20
 
To avoid these ads, REGISTER NOW!

houdni

Well-known member
Joined
Feb 22, 2011
Messages
83
heres the receptacle im using for my welder.. powers a synchrowave 250

IMG_20120206_204339.jpg


IMG_20120304_185428.jpg
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
hp is 5 as the product title says for the compressor, but running amp is 22 amp. The motor is not continuously running but I guess when sand blasting it does.

I would really like to use a plug setup if possible and not breaking code

The welder I want is AHP alphatig 200x

Standard NEMA plugs are rated to about 3HP. So unless u find a plug and outlet that is rated for 5 or more HP, then it needs to be hardwired.

And circuits for motors are wired based on HP.

Wire is sized @ 125% of NEC table FLC.

Dor 5HP u need #10 THHN or #8/2 NM-b aka romex.
 

bry@n

Well-known member
Joined
Dec 29, 2008
Messages
2,785
Location
Ocean County, NJ
So I have a miller 211 and I am wired for 20 amp plugs.

What wire should I use for the miller 211? I have #12 now for the 20amp plugs.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,180
Location
SE MI
The welder is designed to be plugged in to 50a circuits provided the wire is 12 or better. The manuals are really written for electric professionals. If the minimum wire which is 14 then the maximum breaker is 30

The reason why "smaller" welder (like a Miller 211) is wired for a 6-50 is because most welding shops already have a 6-50 outlet installed for bigger welders !

What ever you do, make sure the breaker is sized to PROTECT THE WIRE to the outlet. You would think that a 30A breaker is oversized for 14 gauge wire, but this is where welder "duty cycle" comes in.

IMHO, if you install a 6-50 (L6-50) outlet and the wire and breaker are sized lover than 50A, you should label the outlet for maximum "sustained" current. Not required, but I think it is just a good idea.
 
Last edited:
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
IMHO, if you install a 6-50 (L6-50) outlet and the wire and breaker are sized lover than 50A, you should label the outlet for maximum "sustained" current. Not required, but I think it is just a good idea.

Is it to code to do this? 6-50 receptacle with 30 amp wire and breaker.

It's like putting a 20amp receptacle on a 15 amp breaker circuit which I think most will say it's wrong to do (but won't likely harm anything beside tripping breakers)
 