Ianale
theoldwizard1
SE MI
Is there a limit on how long the ground wire for a sub-panel can be ?
I am adding a sub-panel to my detached garage but would like to put the ground rods on the other side of the garage. That would mean a 30+' ground wire.
wyliesdiesels
Modesto, CA
The wire for grounding electrodes is called a GEC(grounding electrode conductor) not a ground wire.
The ground rods should be installed below the panel. If u ran that wire inside all the way around the building it sets up a fire potential for when lightning strikes or PoCo high voltage lines contact lower voltage lines.
http://www.ecmag.com/section/codes-standards/grounding-electrode-conductors-building
T
theoldwizard1
SE MI
Sorry, I could not remember the correct terminology.
That implies "as close as is reasonably possible".
So if I want the the ground rods on the other side of the garage, I will need to install the panel there.
Any other ideas of installing GEC rods so that they are not above ground in an area where (little kids) ight trip over them ?
bczygan
DETROIT! Arsenal of Scrappers
Another couple of ground rod questions.
Would it hurt or help to install ground rods for a sub panel in an attached garage?
Could you install ground rods in a crawlspace, if you had access?
Can ground rods be installed at an angle rather than vertical?
If you have no ground rods, just attachment to the water pipes, is it good to add them?
Bill
Speedy Petey
NY State
No help IMO.
If installed it would need to be bonded to the main service electrode.
250.50 Grounding Electrode System
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
Yes, nothing in the NEC prohibits it.
Up to 45 deg or buried horizontally if rock is hit.
250.53(G) Rod and Pipe Electrodes.
The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.
It is required. A water pipe electrode must be supplemented by another form of electrode.
250.53(D) Metal Underground Water Pipe.
If used as a grounding electrode, metal underground water pipe shall meet the requirements of 250.53(D)(1) and (D)(2).
(1) Continuity.
Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.
(2) Supplemental Electrode Required.
A metal underground water pipe shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). If the supplemental electrode is of the rod, pipe, or plate type, it shall comply with 250.53(A). The supplemental electrode shall be bonded to one of the following:
1 Grounding electrode conductor
2 Grounded service-entrance conductor
3 Nonflexible grounded service raceway
4 Any grounded service enclosure
5 As provided by 250.32(B)
T
theoldwizard1
SE MI
REQUIRED !
View media item 33304
Well, I don't think you can install an 8' rod in a crawl space. You could install it at an angle and then bend the last foot or 2 straight up ! (I'll never tell !)
Well, not too long a go, that was accepted code, but the ground wire must be continuous back to the meter and be clamped on both sides of the meter.
Richard Cranium
central Washington
Bill my two ground rods lay horizontal in my 3 foot deep trench that my 3 inch pipe is buried in.
So installing them a an angle should not be a problem.
I had a permit and had it inspected and it passed.
Speedy Petey
NY State
REQUIRED !
Not in an attached garage it's not.
Well, "not too long" is a subjective term. In all the time I've known about this stuff, almost 30 years, it was not enough to simply have a single water pipe electrode.
bczygan
I don't see any ground rods outside near the meter box or where the service entrance cable goes in to the panel (Both close to each other).
House built in early 40's, so might not be there.
Bill
Cmreschke
North of Detroit
Agree rod not required on attached structure sub panel. Agree rod required on all services and if it's not there then it should be installed. Cold water bond was never just allowed to be only one there.
Back in the day you just hit closest cold water pipe and jumped the meter with another piece.