Need advice on correcting a poor gas line installation in kitchen

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
So the short story is we are doing a quick kitchen facelift. Granite countertops, tile back splash, new stove.

I removed the built in oven and found this behind it:







:shocking: :mad:

The house was built around 01/02. They cut the drywall and ran the gas line in the wall. They left the drywall open like you see and installed the built in oven.

I will repair the drywall, and make access covers for the electrical junction boxes.

I plan on removing the excess pipe and making it a connection near the floor for the new stove. But I thought you shouldn't run pipe in the wall like that and all joints should be accessible? Should I box it in with 2x4s and then make an access panel that can be removed?

Suggestions are appreciated.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,417
Location
N CA
Wow, in looking at that I finally got one of those flashbacks they promised me back in the 60's. Your plan to bring the gas in low is good depending upon what you are connecting to it. As long as you are going to open the wall I think I would forgo the sheetrock and put a sheet metal cover over the wall and call it good.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
Jack....the wall is open already, that's how I found it. The brown stuff is blown in insulation. I plan on putting the gas shut off valve near the floor, it will be connected to a standard flex line for a gas stove. Basically where you can see the union at the bottom of the picture is where I will add an elbow and ******.

Can anyone tell me if I can (by code/standard) do two 90* elbows so that the valve will run horizontal along the wall?
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,371
Location
Michigan
Jack....the wall is open already, that's how I found it. The brown stuff is blown in insulation. I plan on putting the gas shut off valve near the floor, it will be connected to a standard flex line for a gas stove. Basically where you can see the union at the bottom of the picture is where I will add an elbow and ******.

Can anyone tell me if I can (by code/standard) do two 90* elbows so that the valve will run horizontal along the wall?

Two 90s should be fine, you can have fittings in the wall but not unions, flex connector cannot pass through walls, floors, cabinets, etc.

If I understand your plan correctly you will be good to go.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,417
Location
N CA
Jack....the wall is open already, that's how I found it. The brown stuff is blown in insulation. I plan on putting the gas shut off valve near the floor, it will be connected to a standard flex line for a gas stove. Basically where you can see the union at the bottom of the picture is where I will add an elbow and ******.

Can anyone tell me if I can (by code/standard) do two 90* elbows so that the valve will run horizontal along the wall?

Ok, proof positive. Good flashback
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,846
That is a mess alright. Do you have another gas appliance hooked up with a regulator going through the top corner. Looks like you might have gas cooktop and oven connections there. Are you going back with stove or separate units. A lot of stoves now are dual fuel with gas cooktop and electric ovens. Much better control of oven with electric than with gas in top of line units.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
Thanks, guys. Correct, that is currently hooked to a gas cooktop. I will not reuse that line. We have a new gas stove that will be replacing the built in/cooktop combo.

My main concern is the gas line in the wall and if I should box it in and leave it open/access panel or if I should just drywall everything and make it sealed off with the new drywall.
 

SALIV8

Well-known member
Joined
Dec 11, 2008
Messages
2,114
Location
chicago and s/w michigan
Thanks, guys. Correct, that is currently hooked to a gas cooktop. I will not reuse that line. We have a new gas stove that will be replacing the built in/cooktop combo.

My main concern is the gas line in the wall and if I should box it in and leave it open/access panel or if I should just drywall everything and make it sealed off with the new drywall.

i would be sure to leave the valve easily accessible.
 
To avoid these ads, REGISTER NOW!

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,237
Location
NW Chicago Suburbs
You really should add a sediment trap below the on off gas valve.
attachment.php


Sediment traps are intentionally installed to help prevent sediment in the gas piping from getting into the gas valve or burner area of an appliance and fouling things up. The photo below shows eighteen years of sediment accumulation at the first sediment trap at my own house, which is located on the main gas line just before the pressure regulator.

Sediment-emptied-from-trap-450x338.jpg


But it's really no big deal if you don't...but it could prevent sticky automatic valves down the road.
 

Attachments

  • trap.png
    trap.png
    3 KB · Views: 175

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I suppose "legal" was a poor word choice. Maybe "right" would have been better. I was referring to the 2x4 box duct taped to the front of the 4x4 box...

Tommy
 
Last edited:
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
You really should add a sediment trap below the on off gas valve.

But it's really no big deal if you don't...but it could prevent sticky automatic valves down the road.

Thanks for the advice, I'll try to incorporate that, too.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
I suppose "legal" wasn't a good choice of words. Maybe "right" would have been better. I was referring to the 2x4 box duct taped to the front of the 4x4 box...

Tommy

Yes, I see what you mean...pics are actually deceiving. The tape is old, must have been there to cover the opening. It has a single outlet mud ring properly attached to the double gang box under the outlet cover.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Yes, I see what you mean...pics are actually deceiving. The tape is old, must have been there to cover the opening. It has a single outlet mud ring properly attached to the double gang box under the outlet cover.

I got ya. No problem. Just being typical GJ OCD...:lol_hitti

Tommy
 

pstnbly

Well-known member
Joined
Jul 20, 2010
Messages
766
Location
So. Vermont
That is a hellacious mess. A house is NY state blew up last night and killed all 6 occupants. Workmanship like this demonstrates how that can happen.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
That is a hellacious mess. A house is NY state blew up last night and killed all 6 occupants. Workmanship like this demonstrates how that can happen.

I agree. I'm pretty pissed. It surprises me because the rest of the house is well done. This is the only problem.

To add to it...just tried to shut off the gas valve for the cooktop....and I can't because the knob hits the countertop. Unreal. Once I get the countertops pulled out I can do it but geeze.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
Is that exterior wall ?? Does that insulation need to stay ??

Yes and yes.

On a positive note, when I took the flare fit gas flex line off I found pipe dope on the threads :(

I have it capped for now. Found the main gas valve in the basement so that's a positive. I've figured out how I want to repipe it, and it will include a drip leg (thanks for the suggestion above). I have to get to the hardware store tomorrow and pick up a few pieces.

I did make some progress on the rest of the kitchen, though. Sink and cooktop are out and all of the countertops are unattached. Hopefully I can start the drywall soon.

Thanks to everyone for the ideas.
 
OP
M

MattVette89

Well-known member
Joined
Nov 27, 2014
Messages
2,265
Location
SW Chicago
Worked on the kitchen today and got a chance to fix the problems. Thanks to everyone for the helpful suggestions.

 