I'd probably go with installing a sub panel as this might be the less expensive route due to the lower cost in copper usage. But to answer your question we have to make some assumptions because you weren't clear...
Are all of the following 30A (5HP) rated current?
planner, jointer, table saw, shaper and dust collection
A good cabinet saw could be 5HP but it's likely that the others are 1-3HP, but you didn't say, so assuming everything requires 30A.
I'm also assuming these devices are hard wired and not cord and plug. DId you know that you can get 240V 20A outlets? You can also get them in twist lock, so in theory you could have 1 240V 20A outlet and plug in different pieces of equipment when you wanted to use them. This is not convenient in a woodworking shop, but could be done.
Planer = 2 conductors
Jointer = 2 conductors
table saw = 2 conductors
shaper = 2 conductors
dust collection = 2 conductors
ground wire = 1 conductor
2+2+2+2+2+0=10 ****, that's > 9 wires (the ground wire counts as a 0 as far as current carrying conductors go. 10-20 wires in conduit requires 50% derating, The NEC cares not that you only intend to run 1 machine at a time...
Assuming (cause you didn't clarify) that all equipment draws 30A.
from the 90C temp rating for THHN wire (90C column is used for derating)
10awg=40A X 50%=20A
8awg=55A X 50%=27.5A (close but no cigar)
6awg=75A X 50%=37.5A
OK, this means that each circuit needs to be wired with 6AWG wire and protected with a 30A breaker. You'd need to have 11 6awg conductor in that 1" conduit and you can't. The maximum allowed fill for 1" EMT is 7 THHN 6awg conductors. You'd have to go up to 1.25" EMT to get your 11 6awg conductors in it...
I don't feel like doing the math on the cost of 70-90 feet of 6awg wire X 11 conductors... But it would be more cost effective to put a subpanel close to the loads and just run each tool in it's own 1/2" EMT with 10awg THHN from the subpanel to the tool.
The math changes a little bit if some of the tools are less than 30A, in that case some of the conductors might be able to be 8 or 10awg.. but the 30A circuit (likely the table saw) and the single ground wire would have to be 6awg.
Now if you ran 2 seperate conduits, placing 2 tools (4 wires) in 1 conduit and 3 tools (6 wires) in the other conduit... 4-6 CCC is rated for 80%
10awg=40A X 50%=32A
8awg=55A X 50%=44A
6awg=75A X 50%=50A
Hey, look at that, if you ran 2 conduits you can use 10awg for everything, so 1 conduit would have 6 10awg wires and 1 10awg ground.
the other conduit would have 4 10awg wires and 1 10awg ground.
So I guess if the conduit was free... But even then if it were me I'd go with the subpanel because I could run 4awg aluminum THHN to the subpanel which 4 conductors would fit in your 1" EMT, breaker it at 65A... cutting costs further... and then have a subpanel close by when I needed to add 120V outlets or lights.... I don't have my conduit fill calculation info handy, but you might be able to do 2-2-4-6 THHN aluminum and fit it in your 1" emt. for a 90A subpanel rating, but you'd have to run the diameter and fill calculation.. and I just did enough math for one night.
Brian