Grounding fixture trips breaker

Phrank308

Member
Joined
Aug 27, 2016
Messages
7
I am in the process of replacing the old fluorescent fixtures in my garage and have run into an issue with the last one I installed. When I ground the fixture, even without hot or neutral connected the breaker will trip immediately.

Some background:

Garage had old T12 strip fixtures which plugged into outlets installed in the ceiling. As most of these had died and I wanted more light I replaced them with T8 eight foot tandem fixtures. These fixtures are direct wire and I've connected them at the boxes which used to hold the outlets in the ceiling. I removed the outlets and will plate over the boxes once everything is working. These boxes are all wired together as well. The fixture that is causing a problem is at the end of the circuit. As I said if I attach only the ground with the other wires disconnected and secured with wire nuts the breaker will trip. The fixture is screwed to wood frame so I doubt that it is grounding out anywhere.

I'm not sure what to start checking to determine what to fix. Any recommendations of what to look at?
 
To avoid these ads, REGISTER NOW!

Geobound

Well-known member
Joined
Aug 14, 2016
Messages
95
Location
Ontario
So are you saying that all of the other fixtures work fine, it's just when you try and attach the last one that the breaker trips?

Have you crossed the black/white/green anywhere?

Have you overloaded the circuit?

Perhaps the ballast lead wires have been installed incorrectly?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,012
Location
Modesto, CA
Is the breaker thats tripping a GFCI?

If so then it means u have neutral current leaking to ground through the chassis. It only trips when u hookup the ground wire because the leaking current is finding an alternate path back to the dource and the GFCI sees this as a ground fault....
 
Last edited:

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Is the breaker thats tripping a GFCI?

If so then it means u have neutral current leaking to ground through the chassis. It only trips when u hookup the ground wire because that's the only alternate path....
I am not sure exactly what he is even talking about, He says he has no other wires connected to the light fixture, not the black wire nor the white wire, only the green wire. But when the green wire is attached to the body of the light fixture, the breaker trips. That makes no sense to me. How can the green wire cause the breaker to trip, even if he has crossed the green wire to the black wire? With only wire connected to the light fixture, how can there be a dead short, or any kind of short for that matter? Am I missing something?
 
OP
P

Phrank308

Member
Joined
Aug 27, 2016
Messages
7
This, or one of the wires so shorted to the fixture where it enters the housing.



Shorting on the fixture was my best guess. Not sure how I would have done that when wiring this one up but not the other seven but I am skilled like that ;).

The romex comes in through a knockout in the middle of the fixture with one of those screw down pressure fit grommets. If I over tightened the grommet could it cut through the casing or am I more likely to have just been sloppy when cutting the outer casing and nicked the wires?

That said would a continuity tester identify if this is what's going on or would I be better off just pulling the wire and putting in new to see if that fixed it?


Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!

Geobound

Well-known member
Joined
Aug 14, 2016
Messages
95
Location
Ontario
If you stripped too much of the outer jacket away, and the metal strain relief is touching any exposed wire, then yes that could be your problem.

Are you going out from one fixture into another with a wire lead?

If so and the other fixtures work, then just replace that one lead and see what happens.

Whatever your problem is, it is only tied to that last fixture if the others before it work.

Check the ballast and make sure you were supplied with the proper voltage.

Some ballasts come as a tri-tap ballast (Canada) as 120/277/347, and perhaps you've tied into the wrong leg?

The same would apply in the US, but likely only 120/277.
 
OP
P

Phrank308

Member
Joined
Aug 27, 2016
Messages
7
So just pulled the wire that I had run from the box to the fixture. And sure enough it had shorted through. When I opened it up it looks like the wire got pinched from not laying right and me putting too many turns on the grommet. As you can see it arched right through the wire insulation and the casing.

c2b9635ac8d2400b720347037882f786.jpg


Sent from my iPhone using Tapatalk
 
OP
P

Phrank308

Member
Joined
Aug 27, 2016
Messages
7
Ohh and if I don't have power going to the lights how am I supposed to see what I'm doing [emoji12]


No really the power is off while I'm working it blew the circuit immediately because I have a switch tied to the garage door so the light was live as soon as the breaker was flipped.


Sent from my iPhone using Tapatalk
 