Looking to finish up the electrical service before closing up the garage walls.
We have had a EV in the past (Volt) with a level 2 240v EVSE this had a dedicated 30A feed and a separate EV meter.
On my new garage I want to make provisions for a full on EV as best we can foresee what the requirements will be.
The heaviest draw I see for current vehicles is for a Tesla with the High Amp charging option - 72A
There are a couple of special considerations for derating that I want to review here to make sure that they are right.
The garage is attached to the house, so the cable will be running from the 400A main service to a spot on the garage wall inside a insulated wall- so wiring buried in insulation.
EV charging is considered a continuous load - so wiring and breaker needs to be upsized by 125% - 72A ->90A
Wire used will be SER and in insulation so 60C Ampacity , 72A continous ->1/0 AL, EVSE requires 3 condictors +ECG - > 1/0 1/0 1/0 2 cable. Distance is 30 feet, 90A breaker.
This would be the design required to support the current Telsa EV w/fast charger.
I am thinking that since the cable is so unwieldy and that I would like the ability to use it for welding in the garage - it makes sense to run from the main to a subpanel at the garage wall and leave it at that for future connection to a EVSE and a 50A welder plug now.
So this changes the wiring to 72A continuous and 50A noncontinuous -> 4/0 and a 150A breaker. (might be 3/0 125A ? min for a assembly rated for continuous load).
The good thing I suppose is that if I want capability beyond the Telsa, I could remove the welding circuit and have a 120A continuous feed available.
So my plan is 4/0 4/0 4/0 2/0 150A feed to to a subpanel with just a 50A circuit now.
I used the sizing calculator at http://www.electriciancalculators.com/calculators/wireocpd_ver_1.html for the wiring.
I want to make sure I have the right deratings in there for the insulation as well.
We have had a EV in the past (Volt) with a level 2 240v EVSE this had a dedicated 30A feed and a separate EV meter.
On my new garage I want to make provisions for a full on EV as best we can foresee what the requirements will be.
The heaviest draw I see for current vehicles is for a Tesla with the High Amp charging option - 72A
There are a couple of special considerations for derating that I want to review here to make sure that they are right.
The garage is attached to the house, so the cable will be running from the 400A main service to a spot on the garage wall inside a insulated wall- so wiring buried in insulation.
EV charging is considered a continuous load - so wiring and breaker needs to be upsized by 125% - 72A ->90A
Wire used will be SER and in insulation so 60C Ampacity , 72A continous ->1/0 AL, EVSE requires 3 condictors +ECG - > 1/0 1/0 1/0 2 cable. Distance is 30 feet, 90A breaker.
This would be the design required to support the current Telsa EV w/fast charger.
I am thinking that since the cable is so unwieldy and that I would like the ability to use it for welding in the garage - it makes sense to run from the main to a subpanel at the garage wall and leave it at that for future connection to a EVSE and a 50A welder plug now.
So this changes the wiring to 72A continuous and 50A noncontinuous -> 4/0 and a 150A breaker. (might be 3/0 125A ? min for a assembly rated for continuous load).
The good thing I suppose is that if I want capability beyond the Telsa, I could remove the welding circuit and have a 120A continuous feed available.
So my plan is 4/0 4/0 4/0 2/0 150A feed to to a subpanel with just a 50A circuit now.
I used the sizing calculator at http://www.electriciancalculators.com/calculators/wireocpd_ver_1.html for the wiring.
I want to make sure I have the right deratings in there for the insulation as well.