Generator Plug Question
DocPhilMD
Mid Michigan
A few of you guys might remember about a year ago I received a TON of help installing a generator plug and interlock kit. I thank you for that.
For a variety of reasons, I am considering moving the plug and breaker to the pole building. I have a 200 amp square D panel that is hooked to the pole building via a dual pole 100 amp breaker. And I have another 100 amp panel in the pole building. Can I just move the 30 amp breaker to the garage and run juice into the main panel that way?
My only concern is that this isn't code. I have the interlock kit in place right now but this won't do much with the juice flowing from the garage. I attached pics below.
pattenp
Virginia - USA
In effect you are allowing the gen to back feed the main panel without a means of assuring that the main breaker is disconnected before flipping on the gen breaker at the subpanel. So yes it's not code nor safe.
mike93lx
Richmond, VA
Do not backfeed a panel without an interlock. The one time you forget to shutoff the main will be the time a linesman is working on the service.
wyliesdiesels
Modesto, CA
If u want power in garage and house with generator at garage:
U would have to leave the interlock on the main panel and then get an additional breaker for the subpanel.
Shut the main off slide interlock then go to garage plug in generator turn on breaker and fire up generator.
Whats wrong with generator feeding the garage through the main panel?
D
DocPhilMD
Mid Michigan
I think the issue here is that you can send power through the sub panel and back into the line without having to turn off the main
theoldwizard1
SE MI
DING DING DING !! We have a winner !
Doing what you suggested is nothing more than a fancy "suicide cord".
wyliesdiesels
Modesto, CA
I just realized i wasnt clear in my previous comment.
U would have to leave the interlock in the main panel and slide it over when using the generator in the garage.
Of course this isnt legit since the garage feeder breaker cant br part of the interlock if u want utility power in the garage.
pattenp
Virginia - USA
What do you mean run another cable? From the main panel to the pole building?
If I'm reading you correctly you want the generator to reside in/at the pole building when in use. The only way to do it is leave the interlock in place along with the generator breaker in the house main panel. The generator power inlet located at the house will need to be moved to the pole building by running new wires for the power inlet to the pole building. This way you have the generator located at the pole building but can power circuits at both the house and pole building. I apologize in advance if I'm in left field as to what you are trying to accomplish. I assume when you said pole building and then later garage, they are one in the same.
wyliesdiesels
Modesto, CA
:+1: That was the other idea i had.