Max Usable Distance for MHF Wire

anuccite

Well-known member
Joined
Apr 4, 2016
Messages
129
Location
Richlands, NC
Sparky's:

for 90amp at Garage, What is the Max distance I can go before I need to go to a larger wire (because of voltage drop)? I'm trying to figure out how far away I can put New garage

2-2-2-4 Alu MHF
 
To avoid these ads, REGISTER NOW!

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Sparky's:

for 90amp at Garage, What is the Max distance I can go before I need to go to a larger wire (because of voltage drop)? I'm trying to figure out how far away I can put New garage

2-2-2-4 Alu MHF


Do you have any idea about where you want it? how big is your back yard?
Your # 2 alum MHF is rated for 75 amps at 100', not sure if you are talking about lengths longer than that or not?

90 amp load would require 1/0 alum at a max of 190'
 
Last edited:
OP
A

anuccite

Well-known member
Joined
Apr 4, 2016
Messages
129
Location
Richlands, NC
So I'm looking at right around 125'. As with most I doubt I will need the 90amps, but will breaker it that way in the house.... and 100 at garage.

buried in conduit
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
125' is not an issue.

Real world experience tells me I don't even start worrying about voltage drop on 240 volt feeders until I get out past 200'.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Where are you getting that info from. #2 Al can be over current protected up to 90A. There is no footage rating.

I had plugged the info into the Southwire Voltage drop Calculator, using a 3% VD, I didn't know if he has a 1/4 acre back yard or a 14 acre backyard, I didn't want him trying to run across the globe and expect no consequences from it. I agree he can protect it at 90 amps.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
I had plugged the info into the Southwire Voltage drop Calculator, using a 3% VD, I didn't know if he has a 1/4 acre back yard or a 14 acre backyard, I didn't want him trying to run across the globe and expect no consequences from it. I agree he can protect it at 90 amps.

The southwire calculator uses 60* c ampacities for circuits less than 100a.

Thats how u got the 75'.

That calculator is a little annoying in that regard. I suspect they do it on purpose.

Better to use a different calculator.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
The southwire calculator uses 60* c ampacities for circuits less than 100a.

Thats how u got the 75'.

That calculator is a little annoying in that regard. I suspect they do it on purpose.

Better to use a different calculator.
Ahhh, my mistake, wasn't paying attention, thanks!!
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I have used a couple different sized breakers. Ran a welding shop from one at 225 ft one winter with a 60A on it. I have wired a couple dozen garages this way including a couple busy ones and while we could make a change if we had to never,,,, never had one trip a 60, have never tripped a feed breaker on anything I ever fed with these and have several myself including my house on a 50.
 
OP
A

anuccite

Well-known member
Joined
Apr 4, 2016
Messages
129
Location
Richlands, NC
I want to be clear on something, In trying to source wire locally, HD, Lowes so far..... Both keep giving me URD wire..... I can't find MHF wire.....

I am assuming that if I want to have a single continuous run, that is not going to work, correct? I cannot run URD inside either structure even if in Conduit?

I can order it from wireandcableyourway.com no problem,
 

dtrojcak

Well-known member
Joined
Jan 22, 2017
Messages
50
I want to be clear on something, In trying to source wire locally, HD, Lowes so far..... Both keep giving me URD wire..... I can't find MHF wire.....

I am assuming that if I want to have a single continuous run, that is not going to work, correct? I cannot run URD inside either structure even if in Conduit?

I can order it from wireandcableyourway.com no problem,



Lowe's has MHF, but I only looked for 4/0 as that's what I needed.
Most MHs have more than 90 amp service so you may have a time trying to find it in smaller sizes.
 

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,078
Location
Seacoast New Hampshire
Many places use the terms MHF/URD/USE to refer to the same thing. URD technically is only used outside by utility companies because it is not rated for use in NEC installations. USE is an NEC-rated version of URD. MHF is essentially USE that has a 4th conductor and is rated for burial.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
I want to be clear on something, In trying to source wire locally, HD, Lowes so far..... Both keep giving me URD wire..... I can't find MHF wire.....

I am assuming that if I want to have a single continuous run, that is not going to work, correct? I cannot run URD inside either structure even if in Conduit?

I can order it from wireandcableyourway.com no problem,

Order from online site such as this one

or try local electrical distributor.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Many places use the terms MHF/URD/USE to refer to the same thing. URD technically is only used outside by utility companies because it is not rated for use in NEC installations. USE is an NEC-rated version of URD. MHF is essentially USE that has a 4th conductor and is rated for burial.

You're close but no prize. URD (Underground Residential Distribution) is a type of wire and carries in most cases only a USE insulation rating, hence why it can't be installed inside. MHF (Mobile Home Feeder) type carries insulation ratings of RHH-RHW-USE, so it can also be installed inside along with being direct bury. URD and MHF are not insulation ratings.
 