pancho400cid
Well-known member
I saw the pic below on Linked-In and it made quite an impression on me - thought I would pass it along - I did not find this myself, thankfully......
The pic is a 480 VAC, 3 phase disconnect. If you look, there are micarta hooks that catch a bale on the handle. They pull a spade out and open the circuit for each of the three phases... unless one BREAKS as shown. Note that the spade didn't get pulled for the black wire.
Had the guy who posted the pic on LI just opened the disconnect and gone to work on the downstream equipment - he would have had a very bad day. Wisely, he put a meter on the downstream side of the disconnect as a check, before touching any conductors and found it was still hot.
Depending on what/how the downstream stuff was connected, all three phases could still have been live....
I know a lot of you guys are electricians and know a lot more than I do about electrical work but the pic really drove home the old "check it with a meter first" lesson for me...
The pic is a 480 VAC, 3 phase disconnect. If you look, there are micarta hooks that catch a bale on the handle. They pull a spade out and open the circuit for each of the three phases... unless one BREAKS as shown. Note that the spade didn't get pulled for the black wire.
Had the guy who posted the pic on LI just opened the disconnect and gone to work on the downstream equipment - he would have had a very bad day. Wisely, he put a meter on the downstream side of the disconnect as a check, before touching any conductors and found it was still hot.
Depending on what/how the downstream stuff was connected, all three phases could still have been live....
I know a lot of you guys are electricians and know a lot more than I do about electrical work but the pic really drove home the old "check it with a meter first" lesson for me...