I am planning on installing four 6-50R receptacles for my welders, plasma cutter and future 230V machinery. Most welding equipment I have looked at has a 6-50 plug, regardless of it's input current requirements (for example, my Miller 375 PC needs only 14A) so I want to use the Nema 6-50. I am not interested in sharing a single 50A extension cord for all my machines. The four receptacles would be on one wall, all within 20' of one another.
I am past final inspection, but my goal is to remain code complaint. At this time I have a single run of 6/3 NM to a single receptacle, feed from the shop's sub panel.
I understand welder circuits are a special case and can use smaller wire if labeled as such, but runs are short so I want to use #6 to match the 50A receptacles.
The county I live in uses IRC 2012 and NEC 2011;
IRC E3702.5 Branch circuits serving multiple loads or outlets.
General-purpose branch circuits shall supply lighting outlets, appliances, equipment or receptacle outlets, and combinations of such. Multi-outlet branch circuits serving lighting or receptacles shall be limited to a maximum branch-circuit rating of 20 amperes.
So I believe my best option is to install a sub panel on the existing 6/3 run, and use a 50A breaker and #6 wire run to each of the four receptacle. The panel and breakers aren't that expensive.
Thoughts?
I am past final inspection, but my goal is to remain code complaint. At this time I have a single run of 6/3 NM to a single receptacle, feed from the shop's sub panel.
I understand welder circuits are a special case and can use smaller wire if labeled as such, but runs are short so I want to use #6 to match the 50A receptacles.
The county I live in uses IRC 2012 and NEC 2011;
IRC E3702.5 Branch circuits serving multiple loads or outlets.
General-purpose branch circuits shall supply lighting outlets, appliances, equipment or receptacle outlets, and combinations of such. Multi-outlet branch circuits serving lighting or receptacles shall be limited to a maximum branch-circuit rating of 20 amperes.
So I believe my best option is to install a sub panel on the existing 6/3 run, and use a 50A breaker and #6 wire run to each of the four receptacle. The panel and breakers aren't that expensive.
Thoughts?