what is thin on my air compressor
knied1
I was given a 480V three phase compressor, I am in the process of replacing the motor with a single phase one.
I have a doner compressor that I took the motor starter off of, and I re-built the motor.
the compressor is a 80 gallon with 7.5 HP pump.
I do not know what this thing is. It is next to the pump, and has copper tube run to the pump, and 2 wires to the motor starter.
Thanks for any help.
K
knied1
thanks
where do I wire it to?
I do not see where on the single phase motor starter for it?
or can I just leave the electrical part of it disconnected?
Skin
Boston
They generally get wired to the switch so that when the pressure switch triggers the solenoid opens releasing the head pressure.
K
knied1
So I can wire it to the same terminals as the pressure switch?
Skin
Boston
That I don't know. Might be voltage specific. See if there is any indication on the switch or harness. They're normally closed so you can try powering it up and listing for the solenoid to open. I wouldn't leave it off since its going to dramatically increase the start-up load on the motor but its also a simple enough part to replace if needed.
K
knied1
I looked online, at pictures and kams1973 your correct.... it is a low oil level switch.
The single phase magnetic starter that I'm using doesn't seem to have a place to wire it.
is there a place I can wire it to?
Thanks
kams1973
Amarillo, TX
If it's a normally closed switch, seems like you can wire it in series with the psi switch if the voltage & amperage rating is adequate
K
knied1
OK so ive been running the air compressor off of an extension cord.
Now I want to just wire it up to its own breaker.
I amusing a 30 amp 220V breaker.
and am planning to run 10-2 romex.
anyone see an issue with this?
the run will go from the breaker panel straight up about 7 feet, 30 feet across the barn truss, and then down approximate 12 feet to the compressor.
I know a lot of people prefer THHN, but im just looking to avoid dealing with the conduit.
Thanks again guys.
redmondjp
Redmond, WA
For a 7.5HP motor and that length of circuit run, I'd go with 8/2 NM-B cable, which is $1.49/foot at Home Depot.
md21722
Mt Juliet, TN
Thanks again guys.
Definitely do not use #10 or a 30A breaker!
For a 7.5HP motor, by code you need #8 THHN (in conduit) or #6 NM-b (Romex). Breaker should be at least 40A but can be as large as 100A to prevent nuisance tripping.
K
knied1
THanks again for the fast responses........guess ill just have to not be lazy and run the conduit.
md21722
Mt Juliet, TN
You can use flexible conduit with stranded THHN. :)
Not sure why you don't want to use the Romex.