Meter can and main panel are on a power pole. I will be pulling 200 amps from the pole to the house in an underground feed in conduit. Planning 3/0,3/0,3/0 thwn. What size ground? Is there a single cable option for this? I don't want aluminum.
The contractor wants an exterior panel for all 240 loads and an interior sub panel for all 120 stuff. He wants the interior panel feed with 125 amps. I assume that should be 1/0 ser?
What is a code compliant way to pass wire from interior stud space to an exterior panel? Siding is all Hardie.
Wire will be 10/3 for dryer and hot water heater, 6/3 for stove and a/c and wire to interior sub panel.
Thanks for the help.
Sent from my iPhone using Tapatalk
First off, why is it that the contractor wants anything. Isnt this your home? Is he mandated by local code to do an exterior panel?
Youre best bet is to use individual conductors.
May i ask why u dont want to use AL...
If you look at Table 310.15(B)(16) found
here you will see that 1/0 AL is too small for 120a load. You will need 2/0...
SER can be used in above ground wet locations so u could surface mount it into the side of the panel or bring it into the back of the panel. Will this outside panel be surface or flush mounted?
However, since u said you have a contractor, shouldnt he be the one to figure all this out? Is he a general or an electrical contractor??
I might leave it. It's wired with #10 thwn to an outlet in a weatherproof enclosure. It was fed with a seimens 20 amp breaker. The framing crew asked for it to be swapped for a 30. The only 30 on hand was a square d, which I am told, is ul listed for multiple brands. Regardless, once the feed is made to the house, that square d is coming out and then seimens breaker is going back in.
Sent from my iPhone using Tapatalk
You cant put a 20a outlet on a 30a breaker. That should be changed to a 20a Siemens breaker and another outlet should be added
And SQ D isnt listed for a Siemens panel. No breakers are listed for use in a different brand/make of panel....
There are, however,
classified breakers for use in certain different makes of panels. However, the SQ D homeline breaker you have is not classified for use in the siemens panel.
The info u got is wrong. Or may be misinterpreted since Siemens does make classified breakers for use in SQ D
QO panels...
Best bet is to use the same brand/make and model of breaker for use in the panel unless its an old panel which obviously doesnt apply to you...
I don't see the point in having the two panels separated from each other. Is the sub panel because you will have more circuits than will fit in a 40 space panel? Why put one outside?
I believe 310.15(B)(7) would allow you to use 2/0 copper for your 200A feeder. It apply's to both services and feeders that carry the entire load of a dwelling. The ground would need to be #6. Depending on the situation you may be able to reduce the neutral also.
I cannot think of a cable that would be suitable for your situation. Individual conductors will be easier to pull anyhow. Any particular reason you do not want aluminum?
I've fed temp outlets for construction with 1p 30A breakers too, It's not correct but for temporary use I don't really consider it a big issue.
Look closer @ table 310.15(B)(7) (which has been removed from the NEC). Its for
3 wire dwelling services and feeders. The OPs dwelling feeder is 4-wire because of the disconnect at the pole so 310.15(B)(7) doesnt apply. He will need to use full size conductors...
As for the 30a breaker on a 20a outlet it could be a big deal especially if the wire is #12 and is feeding multiple saws and compressors...I have seen 20a outlets burn up from near 30a flowing through them. They arent rated for 30a...