Yeah...not quite certain I was making a big deal out of anything...just having a conversation and trying to get as much info as I can...that is what I tend to do so I don't frig things up. Sorry if I wasted your time by not immediately taking your advice as the sole solution. Peace out.
I hope it didn't sound like that- it's just that you made no mention of your original issue with the wire as a problem, and Wylie seemed to not know why we were talking about splices, so I thought I should get your take on where that falls as a possible solution for you or why you rejected it or missed those suggestions.
Since you had the six operation issue correct from the start...wasn't sure you were getting anything out of that sidebar.
Sorry
Well, the 2017 code does say, "... to disconnect all ungrounded conductors with no more than six operations of the hand." 225.33(B).
Hmm so does the six breaker thing apply if there is a disconnect in the adjacent panel? Ie a sub located next to the main panel....Anton, the exact same wording in the 2014 NEC also
Hmm so does the six breaker thing apply if there is a disconnect in the adjacent panel? Ie a sub located next to the main panel....
Sent from my Moto G (4) using Tapatalk
I appreciate everyone's suggestions...it has given me several different things to consider. Thanks all.
Hmm so does the six breaker thing apply if there is a disconnect in the adjacent panel? Ie a sub located next to the main panel....
Sent from my Moto G (4) using Tapatalk
It follows what Patten wrote, not a problem.No. As long as all the power in the building can be disconnected at the building by switching off 6 or less breakers at one location. So as long as the sub is killed by the main, and the sub is in the same building as the main, the sub is not limited to 6 breakers.
There is nothing wrong with feeding it from one panel to the other. Why fug around with a Jblock and some other ****, use the first panel as it is, nothing extra needed to add in between, use a breaker to feed the second. Its already in place. This thread has some ideas but a few brain farts too.
If I am not mistaken this was suggested at a cost of 22$ just for for the block, not including an enclosure so he could extend some wire to change to a panel with a main. Another 6 or 8 space panel depending on brand runs about the same cost. Feel free to splain how this can be cheaper and easier than simply adding another cheap panel?
We do this work all the time, most of the ideas some of us give are the most practical, its from some experience. If I looked at some of these ideas after the fact would have to say,,, wtf, some of them may even be legal but its often just poor design, extra work for no gain. They make an 8 space panel in the same box as a 6 just for this purpose, he will lose 2 in the original to feed it but will have 8 in the new to make up for it and a couple additional more free, maybe more when its all done.
This thread was a pretty helpful discussion for me as I am going through a similar situation. I have a sub panel in a detached garage, but the panel is a "load center" with only main lugs, so I have to install a backfed 100Amp breaker as the main. I ran into the same issue, my feeder lines are too short to reach up to the top. Luckily I did a little reading of the included manual and it mentions, just flip the panel over... BINGO, now the main is at the bottom and my feeder lines are long enough to reach the "main".
I also would have the suggested the idea of sliding the panel up or down to provide more slack if you were set on keeping the existing panel. Upgrading to a bigger panel is of course the best option! Good luck!
To cut PVC like that , I have used mason twine (especially dirty, used, mason twine)